Thread: Scaling values in Zenon 8.2
    15.04.2021
    3
    Ausrufezeichen Scaling values in Zenon 8.2
    Hi all,
    I'm polling values from a PLC using DNP3_TG driver. The PLC provides analog values for Phase Currents, Voltages, Power....
    Some of the data needs to be linear scaled down/up by 10 to represent the correct measurement.
    Is there a way to do it in Zenon? I don't want to go through the route of creating a IEC-61131 Zenon Logic to do this.
    Is it possible to adjust the scaling using the linear value adjustment?
    Any leads would be of great help!
    VIKHASH
    1,038
    Default Re: Scaling values in Zenon 8.2
    Variable properties node 'Value calculation':
    - in section 'Value range PLC' - value 1:1 like received from the PLC (so you can left like it is)
    - in section 'Value adjustment linear' - value range you want to scale to.
    - consider the use of property 'Decimal' for fractions.
    example: PLC delivers measured value (REAL/LREAL) of some Voltage in range of DINT
    - decimals = 1
    - value range PLC: min = -2147483648, max=2147483647
    - adjustment: min =-11000.0, max = +11000.0
    As result zenon displays value scaled to 11kV in 0.1V precision
  1. Scaling Issue in Value Calculation
    By AJAY KUMAR CHEKKA in forum Engineering Studio & Service Engine (former zenon Editor & Runtime)
    Last Post: 28th January 2019, 09:01
  2. Scaling Problem
    By tigershark in forum zenon Energy Edition
    Last Post: 20th November 2016, 22:13
  3. Historical Trend Scaling
    Last Post: 7th October 2013, 15:25
  4. y-scaling trendelement
    By affoltep in forum Engineering Studio & Service Engine (former zenon Editor & Runtime)
    Last Post: 22nd July 2009, 13:38