    Frage Scada - plc reconnection

    Hello All,

    I am using a SIEMENS S7 TCP-IP DRIVER to communicate with S7-1200 PLC (ZENON SUPERVISOR) . I am having 3 S7-1200 PLC. PLC1 has 424 tags, PLC2 has 381 tags and PLC3 has 2333 tags. I am facing an issue with the SCADA - PLC Communication Reconnection when the PLC3 disconnects and connects again. The SCADA takes around 5-10 seconds to reconnect automatically to PLC1 and PLC2 (my reconnection time setting is set to 5 seconds), but my SCADA takes 10 minutes to establish communication with PLC3(my reconnection time setting is set to 5 seconds for PLC3 too).

    Case 1
    When I Close my runtime and open again, the SCADA establishes communication immediately with PLC3.
    Case 2
    When I use STOP/START Driver Function my SCADA-PLC Communication reconnection is immediate. with PLC3.

    Is it because the PLC3 tag has a high percentage of variables it takes so much time to reconnect?

    Kindly let me know what might be the cause for the issue and a possible solution for the same. Thanking you in advance.

    Regards,
    Venkataraman.H
    TEAL-AS





  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,025

    Default Re: Scada - plc reconnection

    I suppose you are testing the reconnect times while disconnecting faster as 30s after connection establishing. All zenon TCP drivers, to protect the ethernet network, have extra feature: after connection break and immediat retry fail, the drivers are not again retrying to reestablish the connection before 30s since previous successful connection start.

    So while testing, just wait longer as 30s before you pull out the cable.
    Or pull it out for shorter as ~10ms ;-) No, just joking. Instead to play with physical cables you can use additional software simulating breaks.

  3. #3
    Join Date
    03.10.2020
    Posts
    3

    Default Re: Scada - plc reconnection

    Quote Originally Posted by ursulak View Post
    I suppose you are testing the reconnect times while disconnecting faster as 30s after connection establishing. All zenon TCP drivers, to protect the ethernet network, have extra feature: after connection break and immediat retry fail, the drivers are not again retrying to reestablish the connection before 30s since previous successful connection start.

    So while testing, just wait longer as 30s before you pull out the cable.
    Or pull it out for shorter as ~10ms ;-) No, just joking. Instead to play with physical cables you can use additional software simulating breaks.

    Thank you ursulak for your reply. Will definitely try simulating using software and check the conditions mentioned.



Similar Threads

  1. Creating variables in Scada addin.
    By lsimas3 in forum Add-In Framework
    Replies: 4
    Last Post: 27th May 2020, 15:11
  2. SCADA Runtime Connectivity
    By pauloodwazny in forum Engineering Studio Logic & Logic Service (former zenon Logic Workbench & Runtime)
    Replies: 4
    Last Post: 22nd March 2020, 10:54
  3. SCADA Web Client Starter
    By eden212 in forum zenon Service Engine Operator
    Replies: 2
    Last Post: 8th November 2019, 16:42
  4. Using the Scada.Addin.Contracts API For XML Imports
    By Kyle in forum Add-In Framework
    Replies: 1
    Last Post: 15th May 2019, 07:35
  5. Eplan and Zenon HMI/SCADA
    By vennan in forum zenon Service Engine Supervisor
    Replies: 2
    Last Post: 1st November 2012, 16:23

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •