Thread: 1200 + IEC 61850 device connection to Energy Edition

  1. #1
    Join Date
    28.03.2018
    Posts
    8

    Default 1200 + IEC 61850 device connection to Energy Edition

    Has anyone attempted to connect 1200 plus 61850 devices  to redundant zenon energy edition systems? Is there a front end com device normally used?
    I don't see adding the number of 61850 driver instances required for 20 devices each

    Thanks for any advice

    Dave

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,025

    Default Re: 1200 + IEC 61850 device connection to Energy Edition

    https://forum.copadata.com/showthread.php?8011-How-many-servers-connections-can-be-added-in-a-single-iec-61850-driver-amp-how-many-such-iec-61850-drivers-can-be-in-a-project&highlight=drivers+connections

    https://forum.copadata.com/showthread.php?9230-Driver-creation&highlight=instances+connections


    The limit are not the drivers, the limit would be the performance of this particular core of the CPU where the zenon Runtime (Service Engine) runs the main thread. This load depends on what your project is doing with variables, e.g. alarming, historian, process gateways, API etc. 

  3. #3
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,025

    Default Re: 1200 + IEC 61850 device connection to Energy Edition


    this screenshot shows how it looks in Task Manager when zenon project is designed for quantity of variables and tasks that the main thread of the runtime is occupying the CPU logical core 0 constantly (about 80% load by general high CPU frequency: 2.8 of 3.3 GHz). This system still works stable; but only as long the CPU temperature < 55C. In summer there could be a problem 
    The summary CPU utilization is <10%, so theoretically you could start many more windows applications, like 1000 more instances of a zenon process driver but... you can not. This PC is close at max performance limit just because of main thread coordinating all the process data transfers between modules/services.
    Attached Thumbnails Attached Thumbnails zClient_CPU_load_at_limit.jpg   zClient_CPU_load_at_limit.png  

  4. #4
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,025

    Default Re: 1200 + IEC 61850 device connection to Energy Edition

    solution: zenon project are scalable, you can decentralize it. You can split a too large project to run as multi-project - on few zenon network servers. Help: manual/network ... Multi-Project Administration

Similar Threads

  1. Replies: 3
    Last Post: 16th October 2020, 09:21
  2. Communication with IEC 61850 edition 1 and edition 2 simultaneously
    By joelprasad in forum zenon Energy Edition
    Replies: 2
    Last Post: 6th August 2018, 10:11
  3. Zenon energy edition 7.50 SP0 zendbsrv is not running
    By mehrdad6687 in forum Engineering Studio & Service Engine
    Replies: 2
    Last Post: 22nd December 2016, 14:45
  4. Zenon ENERGY Edition and Runtime
    By aladimurugan in forum zenon Energy Edition
    Replies: 3
    Last Post: 17th November 2015, 02:24
  5. Command function in energy edition
    By misbah in forum zenon Energy Edition
    Replies: 3
    Last Post: 28th February 2012, 11:44

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •