    Default Distrurbance record using IEC-103

    Hi,

    I am trying to download Disturbance record using IEC 103 driver. i can able to download the DR but it is not matching with Disturbance  record downloaded using
    relay software.
    .cfg and .dat files were not as same DR downloaded through relay software.

    Also INF is same for multiple DI , DO, Virtual channels.

    relay used is 7SR224






  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    930

    Default Re: Distrurbance record using IEC-103

    The zenon IEC870_103 (master) driver, if correctly configured, transfers the data recorded in the outstation (in an 103-slave) exactly according the guidelines of IEC 60870-5-103 protocol and converts these received data to the COMTRADE format files. Both protocols are international standards.

    If the result are wrong files, then either your driver configuration has to be improved or the relay is not (fully/correctly) IEC 60870-5-103 compliant. When a relay properly works with the another software of the own manufacturer, it is not guaranteed that it is 100% compliant with the international protocols and then interoperable with software and hardware of other manufacturers.

    I do not know devices "7SR224" and you haven't written what exactly is differ or wrong, or not like expected; thus I'm not able to guess what could be a solution.

  3. #3
    Join Date
    24.04.2016
    Posts
    3

    Default Re: Distrurbance record using IEC-103

    7SR224 is Siemens Relays
     Please Attached project File
    Same has been tested with Siemens 7SJ61 Over Current protection observed the same issue.


    Specially analog Channels data is not correct in .cgf and .Dat file
    Attached Files Attached Files

  4. #4
    Join Date
    24.04.2016
    Posts
    3

    Default Re: Distrurbance record using IEC-103

    Zenon has only provision to inter the INF  in channel 

    while their is Same channel no for binary Input, Binary Output and Other Virtual Bits  with diff function type.

Similar Threads

  1. CEL doesn't record events when loss of connection to RTU
    By cosminbutanescu in forum Drivers
    Replies: 3
    Last Post: 2nd April 2019, 12:36
  2. New AML record
    By diemon in forum VBA
    Replies: 3
    Last Post: 26th May 2015, 14:52
  3. IEC 103 Distrubance Record
    By archie in forum zenon Energy Edition
    Replies: 13
    Last Post: 13th September 2012, 10:08
  4. IEC 103 Distrubance Record
    By archie in forum Drivers
    Replies: 13
    Last Post: 13th September 2012, 10:08
  5. Replies: 3
    Last Post: 12th September 2008, 09:16

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •