Thread: Periodic Synchronization of PLC

  1. #1
    Join Date
    27.08.2020
    Posts
    3

    Default Periodic Synchronization of PLC

    Hi all,
    I'm a beginner on zenon and I would like to send periodically a command of synchronization on driver IEC104 to one or more PLCs (RTUs).
    This command should be sent eg. every five minutes once the link IEC104 with the PLC is up.

    Many thanks in advance for your suggestions.

    Filippo



  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    983

    Default Re: Periodic Synchronization of PLC

    Create T103 variable(s) and zenon function 'write set value' to this variable. In the function activate the option 'directly to the Hardware'. Then link the function in the module Time Control.

  3. #3
    Join Date
    14.09.2017
    Posts
    32

    Default Re: Periodic Synchronization of PLC

    Hello,

    If I Execute T103_Set function for 5 minute interval using time control, does it will affect the any other functionalities in program?
    Example: If I am providing any other Manual command and at same time periodically T103_Set function gets ON whether it affect to the command which I am providing manually?

    Regards,
    Rahul.
    Last edited by rahulindore05 : 2nd November 2020 at 08:25

  4. #4
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    983

    Default Re: Periodic Synchronization of PLC

    Are the modern computers performant enough to do some simple task each 5 minutes

    zenon has a function queue (help: Manual > Functions and scripts > Functions > Execution sequence during Runtime). Each function - the user/project executes - is taken into the queue and then performed. Thus, theoretically it may happen that you configure period of 5 minutes, but it will be executed after 5 minutes and 100 milliseconds instead, e.g. while RT had more as this one function. Anyway, in the ASDU<103> the driver sends the time information of command execution IN DRIVER, nothing what user did, or not did, in the Runtime before.
    Last edited by ursulak : 2nd November 2020 at 14:25

  5. #5
    Join Date
    14.09.2017
    Posts
    32

    Default Re: Periodic Synchronization of PLC

    Thanks for your feedback.

Similar Threads

  1. Day counter for periodic maintenance
    By doublem in forum zenon Service Engine Supervisor
    Replies: 1
    Last Post: 17th March 2020, 09:24
  2. Subproject StandBy server synchronization
    By jurijcadez in forum zenon Network
    Replies: 5
    Last Post: 20th June 2013, 02:02
  3. Time synchronization in reverse direction
    By michael_k in forum zenon Energy Edition
    Replies: 4
    Last Post: 16th February 2011, 10:33
  4. IEC-870 time synchronization
    By okhotnikov in forum zenon Energy Edition
    Replies: 5
    Last Post: 27th August 2010, 13:53
  5. IEC-870 time synchronization
    By okhotnikov in forum Drivers
    Replies: 5
    Last Post: 27th August 2010, 13:53

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •