Thread: Communication Details of IEC60870-5-101

  1. #1
    Join Date
    07.05.2018
    Posts
    20

    Default Communication Details of IEC60870-5-101

    Hi dear experts,

    For IEC-101 driver, I need to show communication status of devices. At zenon editor creating new variable, there is option for plc marker or communication details. I have created variables from predefined variables for communication details, but they are not working properly. How can i get the status of communication? At IEC850 driver, I can get all details.

    Thank you.

    Attached Thumbnails Attached Thumbnails Adsız.png  

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    870

    Default Re: Communication Details of IEC60870-5-101

    The variable on your screenshot - with driver object type 'communication details' contains the number of the configured COM serial port; not the status of the communication.

    In IEC870 driver, while communication via -5-101, the indicator of communication problems are the status bit of variables. If variables have status bit INVALID then the communication is lost (or variable addressing is wrong); when SPONT or GI then the value of variable was received from the device.

    By default, the screen elements linked to variables with INVALID status have in right upper corner a small red square. You can see the status bits of the variable by right-click on the screen element where variable is linked - it opens the context info about the variable. The status bits you can evaluate by reaction matrix linked to the variable and e.g. define an alarm when INVALID.

Similar Threads

  1. IEC62056 Communication details
    By bert.reynders in forum Drivers
    Replies: 1
    Last Post: 5th March 2018, 09:53
  2. IEC60870 Driver Communication Status
    By knubla in forum zenon Energy Edition
    Replies: 1
    Last Post: 29th November 2012, 13:32
  3. IEC60870 Driver Communication Status
    By knubla in forum Drivers
    Replies: 1
    Last Post: 29th November 2012, 13:32
  4. Trend details
    By bojan in forum zenon Supervisor
    Replies: 1
    Last Post: 30th March 2011, 00:00
  5. How to populate details of alarm variables?
    By nahala in forum zenon Supervisor
    Replies: 5
    Last Post: 14th May 2009, 09:06

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •