    Default Process gateway-DNP3

    Hi,

    I have zenon, configured as DNP3 process gateway . In order that DNP3 client will be able to import data, i need to run the zenProcGateway.exe and export data aside from the runtime. Attached is the window that will appear for process gateway.

    When this window is closed by mistake, DNP3 client will not get the data. Seems vulnerable of closing by mistake during operation esp by operators.

    Is their any ways to run this in background or other ways safer during operation.

    thanks,
    Attached Thumbnails Attached Thumbnails Process Gateway-DNP3.jpg  

  2. #2

    Default Re: Process gateway-DNP3

    yes, this is possible. Please also take a look at the help.

    When the process gateway is started with the option "-hide" or "/hide", the gateway is started, and the window is hidden automatically, and can no longer be closed by the user.