    Hello!

    I made simulation using dnp process gateway.

    I have noticed that the data that is being shown in the DNP client is only the whole number value

    here is the scenario:

    SERVER-A IS RUNNING WITH ZENON DNP PROCESS GATEWAY AND SHOWING THE VALUE FOR KILOWATT = 18.26

    AND SERVER-B WITH ZENON AS A DNP CLIENT ( CONNECTED TO SERVER-A THRU TCP) IS SHOWING ONLY THE WHOLE VALUE KILOWATT=18.00 ONLY

    what is the additional configuration on SERVER-B to get this decimal values or exact value from SERVER-A?

    Thanks!

  2. #2

    Default Re: DNP- Process Gateway

    what object type are you using? As far as I could see in the DNPv3 standard, e.g. Analog Input (Data Object 30, any variation) does not support floating point values with decimals.

  3. #3

    Default Re: DNP- Process Gateway

    the data object type 100, short floating point, does support a true float value, however this data object type is currently not supported by either our driver or the DNP3 process gateway.

  4. #4
    Join Date
    29.08.2009
    Location
    LEGAZPI CITY
    Posts
    56

    Default Re: DNP- Process Gateway

    Im using analog type...

    i have to get the decimal points not the whole number..my main concerned are the analog points with only decimal values. for example the power factor

    in SERVER-A the value of power factor is .89

    but in SERVER-B it shows 0 zero value.SERVER-B is not reading the decimal points..


  5. #5
    Join Date
    29.08.2009
    Location
    LEGAZPI CITY
    Posts
    56

    Default Re: DNP- Process Gateway

    Quote Originally Posted by markclemens View Post
    the data object type 100, short floating point, does support a true float value, however this data object type is currently not supported by either our driver or the DNP3 process gateway.

    it means we cant get the decimal values?

  6. #6

    Default Re: DNP- Process Gateway

    yes unfortunately this is exactly what it means. The zenon DNPv3 process gateway currently does not support the data object type 100. Also the zenon DNPv3 driver currently does not support it.

    Please contact your sales representative if you need this functionality really badly or very urgently.

  7. #7

    Default Re: DNP- Process Gateway

    if it is not urgent, but you would like to see this in a future release of zenon, contact your support representatives for them to bring in your feature request. It will be processed and discussed by a team of experts, whether or not to implement this in a future version.

Similar Threads

  1. Process Gateway IEC870SL
    By lunzer in forum Drivers
    Replies: 7
    Last Post: 8th August 2017, 12:28
  2. Zenon process gateway.
    By murphys in forum Drivers
    Replies: 6
    Last Post: 14th January 2010, 13:17
  3. Process Gateway
    By hoscillada in forum Drivers
    Replies: 12
    Last Post: 8th November 2009, 22:57

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •