Thread: zenon EE 7.2 iec-61850 communication

  1. #1
    Join Date
    06.11.2019
    Posts
    1

    Default zenon EE 7.2 iec-61850 communication

    For now we have been in trouble to processing YANBU phase 3 project regarding IEC-61850 communications in SaudiArabia

    1. a matter for phenomenon>>

    We are communicating about 100~150 IEDs from one Server by using ZENON EE 7.2 ver.>>
    While we are communicating ABB REF542 a problem comes up now, however when it works rightly the data is transmitting properly, too.

    Though, When IED Power turn off or delete LAN CABLE 
    it doesn't recover automatically.
    RCB it can't be enabled.

    2. test

    We been repeated on/off three of(IED) at the same time, we recover them three out of ten times randomly.
    And also the rest of 7 times it didn't recover
    We need to check about wireshark capture and diagnosis log.
    Attached File on email.

    Zenon driver : setup status
    Polling : 500ms
    IP : 10.50.11.245
    SUBNET 255.255.255.248


    IED IP address>>
    10.50.12.90>>
    10.50.12.91>>
    10.50.12.92

    wireshark & logfile
    http://bigfile.mail.naver.com/bigfileupload/download?fid=UXFZ16+GW4YjK3YZaAiGFAtXFxtma3YZKAulK xgqKxUwFxMqF3YwFxb9KxU9axvlHrMrFqtqK6KwMxICFqJvaxu Zpoi4FxiCKoKmM4k0FA0S>>

    I am looking forward to your quick response



  2. #2
    Join Date
    28.02.2013
    Posts
    163

    Default Re: zenon EE 7.2 iec-61850 communication

    Dear nafunky7,

    when trying to open that link an error message shows up, that the request is invalid.

    However sharing network traces and logs via this public forum might not be the best option as they may contain confidential or sensitive information.

    Please check the link and contact our support team via email!

    Best regards,
    Felix

  3. #3
    Join Date
    16.02.2018
    Posts
    5

    Unglücklich Re: zenon EE 7.2 iec-61850 communication

    please tell me if you find a solution!

    i know this Problem too.

    the problem appears when the abb devices make a restart and zenon do not reqognize this becaue the restart happens very fast

    Thanks!

  4. #4
    Join Date
    28.02.2013
    Posts
    163

    Default Re: zenon EE 7.2 iec-61850 communication

    Dear Mr. Gruber,

    please also contact your local support representative and provide zenon-logs, wireshark logs and details about zenon version, ABB device etc.

    So we can analyze your issue in detail.

    Regards,
    Felix



Similar Threads

  1. Problem with ReMa, 61850 Report communication and delay time
    By doublem in forum zenon Energy Edition
    Replies: 5
    Last Post: 18th April 2019, 13:41
  2. Replies: 3
    Last Post: 11th September 2018, 13:00
  3. Replies: 1
    Last Post: 28th August 2018, 08:45
  4. Communication with IEC 61850 edition 1 and edition 2 simultaneously
    By joelprasad in forum zenon Energy Edition
    Replies: 2
    Last Post: 6th August 2018, 10:11

Tags for this Thread

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •