Thread: Converting of IEC61850 integer values into Bit wise

  1. #1
    Join Date
    12.05.2019
    Posts
    2

    Default Converting of IEC61850 integer values into Bit wise

    Dear 
    We have almost 900 IED in a project each having four function blocks to combine digital alarms and send it as integer value via 61850 to Zenon.
    1-I need to know if Zenon logic has a standard Function blocks to reconvert the integer values back to bit wise that i can define them as  alarms.
    2-If with this number of IEDs, Do i need to run Zenon logic in a separate PC.


    Example of the function block available in the IED, which convert 16 bit alarms into integer value.

    Regards,
    Adel 
    Attached Thumbnails Attached Thumbnails 16BIT_to_wordFB.PNG  

  2. #2
    Join Date
    18.08.2015
    Posts
    3

    Default Re: Converting of IEC61850 integer values into Bit wise

    Dear Adel,

    You can use the functions SERIALIZEOUT to get the bit values from the integer variable and SERIALZEIN to store them to other variables, e.g. STRATONNG variables which can be configured to create the alarms in zenon.

    zenon Logic Workbench documentation:
    IEC 61131-3 Programming Environment > Programming - Reference guide > Advanced operations > SerializeOut
    IEC 61131-3 Programming Environment > Programming - Reference guide > Advanced operations > SerializeIn



    There is hardly one definitive answer to your second question.
    This strongly depends on the system ressources (memory, cpu, ...), ressource use (other applications), and the intended zenon topology (zenon version(s), one or more projects active, redundant servers, number and activity of connected clients, ...) and functionality (archiving, reporting, alarm evaluation, number and rate of events from the IEDs, ...).

    Best regards,
    Leo

  3. #3
    Join Date
    12.05.2019
    Posts
    2

    Default Re: Converting of IEC61850 integer values into Bit wise

    Hi Leo

    The architecture contains two redundant servers and zenon Web-server all are installed in virtual environment.
    1- in this case does an additional server is enough to run zenon logic on it, or do i need redundant servers to improve system availability ?



    Regards,
    Adel.

Similar Threads

  1. Shift wise Alarms/Audit Trail
    By SRI in forum zenon Supervisor
    Replies: 0
    Last Post: 15th October 2019, 09:42
  2. converting from 5.5
    By aleb2 in forum zenon Supervisor
    Replies: 6
    Last Post: 28th October 2015, 21:53
  3. Issues in Screens when converting from 6.21 to 7.2
    By salmanhassan2 in forum zenon Supervisor
    Replies: 4
    Last Post: 3rd September 2015, 08:34
  4. Converting Main Program to UDFB
    By sidramsatyal in forum straton / zenon Logic
    Replies: 2
    Last Post: 25th October 2013, 08:53
  5. convert 2 integer into 1 float
    By jahidbagwan in forum zenon Supervisor
    Replies: 3
    Last Post: 17th October 2013, 22:36

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •