    Default Stop alarms during no production

    Hi,

    I have created some alarms from the machine and grouped them machine wise and I want to stop all those alarms during weekends and only during shift running. I am thinking to create the function alarm active/inactive is it the best practice or any other method to be followed.


    Regards
    Sandeep

  2. #2
    Join Date
    25.06.2012
    Posts
    126

    Default Re: Stop alarms during no production

    Hello sandeep2018,

    Yes that would be a good solution, you can integrate the function alarm active/inactive with the Production and Facility Scheduler module so that switching of the respective alarm groups relates directly to the start and end of shifts, but also weekends/holidays, etc.

    Find more in zenon documentation topic Manual > Production and Facility Scheduler.

    Good luck.

    Best regards,
    David Cerdeira

  3. #3
    Join Date
    28.03.2018
    Posts
    35

    Lächeln AW: Stop alarms during no production

    Hi,

    Thanks and its working

    I am also facing two issues so they are

    1.Created one screen for scheduler and schedules and no luck
    2.Created one screen and display it on main screen via start screen function- 1 just alert to display

    Regards
    Sandeep

  4. #4
    Join Date
    28.03.2018
    Posts
    35

    Default AW: Stop alarms during no production

    Hi,

    This is done via a straton logic variable and enabling it during shift running so that only alarms during shift run will be captured

    Regards
    Sandeep

  5. #5
    Join Date
    25.06.2012
    Posts
    126

    Default Re: Stop alarms during no production

    Hello Sandeep,

    1.Created one screen for scheduler and schedules and no luck 
    2.Created one screen and display it on main screen via start screen function- 1 just alert to display 
    I am not sure if I understand correctly both situation but let me try:
    1) Sometimes users forget to disable the flag below in the editor, so that the scheduler runtime files are not compiled and thus this module does not work in the runtime.



    2) You can limit the alarm to 1 historical data in the screen switch function to the AML (this includes active/ring buffer alarms). As below.



    Good luck.

    Best regards,
    David Cerdeira
    Attached Thumbnails Attached Thumbnails 2019-06-19_16h15_23.png   2019-06-19_16h26_10.png  

  6. #6
    Join Date
    28.03.2018
    Posts
    35

    Default AW: Stop alarms during no production

    Hi,

    Alarm issue solved by interlocking with shift timing and scheduler let me try again by un checking the flag even though I tried before

    Regards
    Sandeep

Similar Threads

  1. no stop code 'Do while'
    By gyu in forum VBA
    Replies: 2
    Last Post: 22nd June 2017, 07:45
  2. Production & Facility Scheduler: Unhandled Exception Error
    By drehpet in forum zenon Supervisor
    Replies: 1
    Last Post: 14th October 2016, 08:58
  3. Stop continuous tone after ack. alarm
    By tihomir in forum zenon Supervisor
    Replies: 1
    Last Post: 26th March 2014, 06:58
  4. CEL 'Stop' button
    By nurul in forum zenon Supervisor
    Replies: 8
    Last Post: 11th August 2009, 09:16
  5. How to Stop Logging Alarms
    By matholton in forum zenon Supervisor
    Replies: 2
    Last Post: 29th September 2008, 11:24

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •