Thread: Command Processing with USINT data type from a DNP3.0TG driver
    07.09.2016
    Beitrag Command Processing with USINT data type from a DNP3.0TG driver
    I would like to ask on how I would configure command processing for Close/Trip command of a breaker.
    From the zenon energy edition training that I attended, they have used IEC61850 driver and BOOL data type.
    Right now, the controller of the breaker we are using only accepts Trip (value = 129) and CLOSE (value = 65) since it only works on USINT data type.
    Will there be any difference on how to configure the command processing? Because I  noticed  that on the Action node of the Command Group the command value available only is 1 and 0 for ON and OFF respectively.
    Please advise.
    Thanks,
    Randy
    17.03.2016
    43
    Default Re: Command Processing with USINT data type from a DNP3.0TG driver
    Randy,
    You need to set the 'use qualifier of command' in the command processing for each of your controls.
    Set the qualifier to 2 to use trip/close.
    See the manual page for "DNP3_TG driver > Creating Variables > Driver objects and types > Mapping of Data types" the Binary Outputs section covers it.
    Hope that helps.
    Dave
  1. Replies: 3
    Last Post: 14th February 2018, 09:48
  2. IEC61850 Driver - Data Type
    By andrea.ornago in forum zenon Operator
    Last Post: 11th October 2017, 08:48
  3. Aditional command butons in command processing screen
    Last Post: 6th February 2017, 09:52
  4. Command Processing