Thread: IEC104 General Interorgation

  1. #1

    Default IEC104 General Interorgation

    Hi
    I need to send command GI from Zenon 104 master per hour. In manual that "By creating command execute with TYPE=100, QULIFIER=20 (VALUE=TRUE or FALSE), you can start a general interrogation manually " so this is in command processing. But it can not assign to time control. Is a function to send command processing ? 

    Brgds

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    790

    Default Re: IEC104 General Interorgation

    Create a variable with type ID 100. Then create a zenon function 'write set value' linked to your T100 variable and set value 1 with 'direct to Hardware' option. Then link this function in the Time Control module.

    To process GI you do not need the Command Processing module (as there is no particular response variable there).
    Last edited by ursulak : 11th June 2019 at 08:18 Reason: completed