Thread: reload driver

  1. #1
    Join Date
    25.09.2009
    Posts
    38

    Default reload driver

    Hello

    how to set settings that after start, stop IEC 101-104 driver procedure SCADA remember last used values and status bits (AVALUE.....)

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    810

    Default Re: reload driver

    Why do you need it?
    Why you want to stop/start the iec870 driver and you don't want to have in your variables that was comes after re-connect from General Interrogation? Each kommunication start in IEC 60870 Standard demands a GI at first.

  3. #3
    Join Date
    25.09.2009
    Posts
    38

    Default Re: reload driver

    we have 2 gateways, we every second check ping and no ping we restart driver with another IP address, but if we set some point in (AVALUE=1) after driverl reload we have (AVALUE = 0)

  4. #4
    Join Date
    25.09.2009
    Posts
    38

    Default Re: reload driver

    it is impossible not stop driver but only change IP address?

  5. #5
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    810

    Default Re: reload driver

    As I remember you are switching TCP/IP configuration of the driver to secondary IP (of the same end-device) to manually shorter switch-over timeout by communications problems.
    So you are intentionally not using redundancy mechanism build in the driver.

    It is the consequence - you are losing some status bits. I will thing over how to help you, but I need time.
    But I think, the simplest would be to keep using secondary IP in driver configuration.