Hello José Luis Torres,
Let me phrase what is written in the help in a different way.
When this is a non-critical communication, when you are OK with the fact that the communication may fail at any given time, without the OPC2Cli32 driver noticing right away, when you are OK with the fact that after communication failure or restart of the OPC Server, there may not be automatic reconnect and when you are OK with the fact that it may be necessary to restart both the system with the OPC client driver (zenon runtime) and the system with the OPC server, and when you are OK with the fact that advanced DCOM configuration in Windows is required, and when you are OK with the fact that a future Windows Update may require you to make changes and when you are OK that there will be no support for configuring DCOM or any issues with the OPC2Cli32 driver while using DCOM, you are free to give it a try. Since we do not recommend it and officially do not support it, there will be no guarantee that you can make it work although technically it might.
I'd suggest contacting your local COPA-DATA support to look again what alternatives there may be.
Best regards,
Mark