Thread: reading memory bits in zenon energy edition from Delta 12SE PLC

  1. #1

    Default reading memory bits in zenon energy edition from Delta 12SE PLC

    Hi Guys,

    I am able to read Holding registers from my DELTA 12SE PLC using Modbus Energy driver with offset of 4097, however I am struggling to read memory bits using Modbus Energy driver. I use Coil and offset of 2049 for memory bits according to delta datasheet. I am not getting anything and there is no error.

    looking forward for your help.


    Regards
    Lingelethu.

  2. #2

    Default Re: reading memory bits in zenon energy edition from Delta 12SE PLC

    Hi Lingelethu,

    When you can read holding registers OK, it seems the general settings, like modbus slave ID / unit identifier, should be correct. I don't have the datasheet of this specific PLC, but I did find something possibly for this type of device, where it seems the Modbus Coil addresses don't start at 0 and also there are gaps in the modbus coil  addressing. Possibly, the coil address you are trying to read, does not exist.

    Have a look at the log files recorded by the zenon diagnosis server, using the zenon diagnosis viewer to see if there are any errors.

    Best regards,
    Mark

  3. #3

    Default Re: reading memory bits in zenon energy edition from Delta 12SE PLC

    Thanks Mark,

    I saw my mistake, I created structured element for my memory bits. Zenon does not like that. I had to create each variable for a memory bit. read coil and bool(not using my structure element I created). 

  4. #4
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    831

    Default Re: reading memory bits in zenon energy edition from Delta 12SE PLC

    >I created structured element for my memory bits. Zenon does not like that. I had to create each variable for a memory bit. read coil and bool(not using my structure element I created).

    I do not agree with this opinion about what zenon likes (or not)
    If in zenon Editor you create a structure of items, e.g. few BOOLs, then in the Runtime this will be anyway spited (internally) to the list of single variables - each representing one item in the structure. So in the Runtime, it does not meter if these coils are separated, independent variables or if they are items in one structure. But the Addressing DOES mater. If you are using a structure you have to take care that the setting of the data type (and then variable) in the property groups 'structure options' and 'addressing' are resulting than in the addresses of the right coil offsets for each item. And this is only possible if a structure gathers coils of following offsets, so without "jumps", gaps etc. 

  5. #5

    Rotes Gesicht Re: reading memory bits in zenon energy edition from Delta 12SE PLC

    I do not agree with this opinion about what zenon likes (or not)

    Sorry for that statement. now I understand.



Similar Threads

  1. Zenon energy edition 7.50 SP0 zendbsrv is not running
    By mehrdad6687 in forum Editor and Runtime Setup
    Replies: 2
    Last Post: 22nd December 2016, 14:45
  2. Zenon ENERGY Edition and Runtime
    By aladimurugan in forum zenon Energy Edition
    Replies: 3
    Last Post: 17th November 2015, 02:24
  3. Writing and reading bits from\to Word
    By masonpiotr in forum VSTA
    Replies: 1
    Last Post: 29th January 2015, 09:00
  4. Command function in energy edition
    By misbah in forum zenon Energy Edition
    Replies: 3
    Last Post: 28th February 2012, 11:44
  5. Reading "M" bits in Siemens
    By scotttee in forum Drivers
    Replies: 1
    Last Post: 24th September 2009, 08:45

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •