Thread: IEC 60870-5-101_104 Value Write Issue

  1. #1

    Default IEC 60870-5-101_104 Value Write Issue

    Dear Support Team,


    We are set an setup of IEC 60870-5-104 Straton as Slave and browsing variables using Zenon IEC 60870-5-101_104 driver as Master. All Tags are communicating perfectly between Master and Slave, but could not write value from Master (Zenon). We have found following Error in execution. Kindly provide solution as soon as possible.

     
    Warm Regards

    Srikanth G
    Attached Thumbnails Attached Thumbnails Diagose error for Master configuration - Copy.png  

  2. #2
    Join Date
    28.02.2013
    Posts
    119

    Default Re: IEC 60870-5-101_104 Value Write Issue

    Dear Srikanth,

    in IEC 60870 there are special variable types for communicating either in monitoring (from slave to master) or in command (from master to slave) direction.

    It seems that you are trying to write a value (on master side) to a variable that is for monitoring which is not allowed.
    Please configure an additional variable in command direction for writing values to the slave.

    Best regards,
    Felix

  3. #3

    Default Re: IEC 60870-5-101_104 Value Write Issue

    Dear Felix,

    We have done Fieldbus Configuration : IEC60870 slave as per attachment and Created Variables " T45 Single command " as a type identification COA=1,IOA =5. When we are trying to browse from Master (Zenon Driver) IEC 60870. respective variable is not browsing (invisible) .

    we cant even see variables from T30 in the master browsing .


    Warm Regards

    Srikanth G
    Attached Thumbnails Attached Thumbnails IEC60870 Import variable list - File.png   IEC60870 Configuration File.png  

  4. #4
    Join Date
    28.02.2013
    Posts
    119

    Default Re: IEC 60870-5-101_104 Value Write Issue

    Dear Srikanth,

    due to protocol restrictions for IEC 60870 the online browsing for variables only works for variables in monitoring connection.
    Types like T30 need to be configured manually on zenon side.

    Please refer to the driver docu for details:IEC870 > Creating variables > Creating variables by importing > Online import

    Regards,
    Felix

Similar Threads

  1. Write set value retentive
    By navaneet in forum zenon Supervisor
    Replies: 2
    Last Post: 14th November 2014, 12:47
  2. Write value on login/out
    By dlamarche in forum zenon Supervisor
    Replies: 1
    Last Post: 6th September 2013, 00:31
  3. Can I write a DynProperties in Runtime?
    By fransiska in forum VBA
    Replies: 4
    Last Post: 29th August 2013, 04:51
  4. IEC 60870-5-101_104 startup
    By lunzer in forum zenon Energy Edition
    Replies: 2
    Last Post: 21st April 2010, 14:47
  5. IEC 60870-5-101_104 startup
    By lunzer in forum Drivers
    Replies: 2
    Last Post: 21st April 2010, 14:47

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •