Thread: S71200 error
    28.03.2018
    54
    Default S71200 error
    I have created a sample project in TIA V13 and tried to communicate with Zenon 8.0 but no communication. Attached the diag viewer
    15.11.2016
    108
    Default Re: S71200 error
    Hi Sandeep,
    It seems you are using the S7TCP-IP driver and not the S7 Driver for S7-1500/1200
    BR,
    Georg
    28.03.2018
    54
    Default AW: S71200 error
    Hi georg,
    When I select S7 driver for S71200 I am not able to select PLC marker as there is only 2 options ie communication variables and symbolic variables
    Regards
    Sandeep
    15.11.2016
    108
    Hi Sandeep,
    If you have a S7-1200 PLC but want to use the S7TCP32 driver, you have to check these things:
    PLC:
    - PUT/GET enabled
    - Datablocks with variables used in zenon: deactivate optimised datablock access
    driver:
    - remote TSAP: 02.01
    Hope this helps.
    If need more detailed help, please consult you local zenon support.
    BR,
    Georg
    28.03.2018
    54
    Dear Georg,
    Thanks for the response, I was just trying to test communication between Zenon and S71200 PLC with a simple logic by using PLC Marker bits, I ve enable the PUT GET from cpu properties and still no result. May be the variable configuration is not correct.
    Regards
    Sandeep
    28.03.2018
    54
    Issue has been solved after doing some correction in the variable addressing, Now I am able to communicating with S71200 by using S7TCP/IP protocol.
    Thanks for the support
    Sandy
  1. Replies: 2
    Last Post: 19th May 2018, 06:19