Thread: Checking communication presence with secondary IP address(device) while primary communication is established

  1. #1
    Join Date
    10.05.2017
    Posts
    58

    Frage Checking communication presence with secondary IP address(device) while primary communication is established

    Hello team,

    In many of the drivers, we have option to enter a secondary IP address/ redundant IP address. In my case IEC 60870 client driver.
    My requirement is, while my SCADA is communicating with the primary IP address in the driver, I want to check the healthiness of the secondary IP address at regular time period.
    If not healthy I want to create a event/alarm.



    Please suggest on this.
    Regards,
    Joel

  2. #2
    Join Date
    13.08.2013
    Posts
    56
    Best Answer

    Default Re: Checking communication presence with secondary IP address(device) while primary communication is established

    Quote Originally Posted by joelprasad View Post
    Hello team,



    In many of the drivers, we have option to enter a secondary IP address/ redundant IP address. In my case IEC 60870 client driver.

    My requirement is, while my SCADA is communicating with the primary IP address in the driver, I want to check the healthiness of the secondary IP address at regular time period.

    If not healthy I want to create a event/alarm.







    Please suggest on this.
    Hi,
    you have some options.
    Probably the best would be the SNMP
    Driver, next to Pingstate one can monitor the whole network e.g. state
    of a port on a networkswitch.
    further reading SNMPNG32 > Creating variables > Driver objects and datatypes > Driver objects |Ping status

    Another option would be to use the programming interface (VSTA/Addin), for reference check https://docs.microsoft.com/en-us/dot...ramework-4.7.2

    Best regards
    Sigi




  3. #3
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    673

    Default Re: Checking communication presence with secondary IP address(device) while primary communication is established

    Only if 870-slave (PLC) would support redundancy according Edition 2 of IEC60870 standard - then you may activate the special redundancy mode in iec870 driver (checkbox in driver settings) and the driver will open both sockets simultaneously. And only then the driver will know all the time, if both IPs are available and healthy; and you could evaluate this info on additional 'status of data link layer' variable - T00, COA 0, IOA 1.
    Without redundancy according 870 Edition 2 it is not possible to check availability of connection basing on IEC60870 protocol. Thus, the iec870 driver opens the TCP socket for secondary IP first when the primary IP is broken. That's why you would have to use another protocol (so, another driver), e.g. SNMP - like Sigi proposed.


  4. #4
    Join Date
    10.05.2017
    Posts
    58

    Daumen hoch Re: Checking communication presence with secondary IP address(device) while primary communication is established

    Quote Originally Posted by ursulak View Post

    Only if 870-slave (PLC) would support redundancy according Edition 2 of IEC60870 standard - then you may activate the special redundancy mode in iec870 driver (checkbox in driver settings) and the driver will open both sockets simultaneously. And only then the driver will know all the time, if both IPs are available and healthy; and you could evaluate this info on additional 'status of data link layer' variable - T00, COA 0, IOA 1.
    Without redundancy according 870 Edition 2 it is not possible to check availability of connection basing on IEC60870 protocol. Thus, the iec870 driver opens the TCP socket for secondary IP first when the primary IP is broken. That's why you would have to use another protocol (so, another driver), e.g. SNMP - like Sigi proposed.


    Thank You Ursula & Sigi
    Regards,
    Joel

Similar Threads

  1. Communication with AB PLC
    By sandeep2018 in forum zenon Supervisor
    Replies: 0
    Last Post: 10th August 2018, 14:13
  2. Communication with same LN/Net address/Driver name
    By azami in forum zenon Energy Edition
    Replies: 2
    Last Post: 29th June 2018, 15:01
  3. communication with s7
    By ameic in forum Drivers
    Replies: 1
    Last Post: 8th September 2015, 15:41
  4. EIB KNX communication
    By seb5167 in forum zenon Network
    Replies: 1
    Last Post: 13th October 2011, 03:13
  5. Communication problem with DNP3 device
    By roberto1978 in forum Drivers
    Replies: 0
    Last Post: 16th January 2011, 20:49

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •