Thread: Siemens PLC to Zenon - Variable update time delay in S7TCP driver - Profinet network

  1. #1
    Join Date
    17.04.2017
    Posts
    16

    Ausrufezeichen Siemens PLC to Zenon - Variable update time delay in S7TCP driver - Profinet network

    Hello,

    In my project i am using Siemens CPU 319 and in zenon S7TCP driver was used to communicate with PLC in Profinet network. Total 4200 PLC variables are created in Zenon. Out of 4200 variables 1200 variables are used as permanently read variable.

    I am getting a delay in variable update in zenon. Whenever a string value changed in PLC and it is getting update in Zenon after 7 SEC and this delay is not consistent. Some times it is taking more than 30 SEC to update the variable values. I have tried with Global update time as 1000 ms and the status was same. If i tried with priority in variables as normal with 500 ms then the status was good and for highest priority with 100 ms also working fine.

    If i tried the same PLC network with less zenon variables then the status was good. If variable was increased then the update timing is varying in zenon.

    So Please clarify me on below points,

    1. How to set/adjust the Global update time or priority for variables to poll the data from PLC faster as possible for more than 5000 tags. Expected update time would be 1 sec.
    2. Is there any relation between permanently read variable setting and tag update with priority setting.
    3. If i create a multiple S7TCP driver instance for a same PLC then it will update the variables faster then a single driver instance. Please confirm.


    Regards,

    Dhanapal








  2. #2

    Default Re: Siemens PLC to Zenon - Variable update time delay in S7TCP driver - Profinet network

    Hello Dhanapal,

    First thing you will want to check is to see if you have any errors logged in the log files of the diagnosis server, whenever you experience the long update times. A variable configured in zenon that does not exist in the PLC or is shorter (different data type, shorter string length) in the PLC than in zenon, is a common cause for communication delays.

    Best regards,
    Mark

  3. #3
    Join Date
    17.04.2017
    Posts
    16

    Default Re: Siemens PLC to Zenon - Variable update time delay in S7TCP driver - Profinet network

    Quote Originally Posted by markclemens View Post
    Hello Dhanapal,

    First thing you will want to check is to see if you have any errors logged in the log files of the diagnosis server, whenever you experience the long update times. A variable configured in zenon that does not exist in the PLC or is shorter (different data type, shorter string length) in the PLC than in zenon, is a common cause for communication delays.

    Best regards,
    Mark
    Hello Mark,

    Thank you for your reply. I have checked for the error in diagnostic viewer and found no error. In this case the tag updation was behaving differently for Global update and Priority tags. When i given priority as normal with 500 ms rate then the variable update was good. If i have more variables (in my case it is 4500 variables) then the updation time was varying.

    Please confirm me whether i have to increase the variable update time if number of variables are increasing.

    Regards,
    Dhanapal



Similar Threads

  1. Zenon to Siemens PLC Tag writing delay
    By Dhanapal in forum zenon Supervisor
    Replies: 1
    Last Post: 22nd August 2018, 10:21
  2. Update variable in Zenon
    By dobryraul in forum zenon Supervisor
    Replies: 1
    Last Post: 15th December 2015, 08:11
  3. S7TCP Driver IP Address
    By ronmany in forum Drivers
    Replies: 1
    Last Post: 4th July 2013, 12:23
  4. Replies: 1
    Last Post: 1st September 2011, 23:30
  5. Replies: 0
    Last Post: 21st August 2007, 09:23

Tags for this Thread

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •