    Default Zenon to Siemens PLC Tag writing delay

    Hello,

    In my project i have used Siemens CPU 319 and it is connected with Zenon Supervisor. With PLC i have connected many devices via profinet and Zenon supervisor too. Total no of PLC tags is 4500. Here i have recipe (RGM) and datalogging to MSSQL using VSTA. 

    When i download a recipe (300 Tags) or write data (around 350 Tags) from zenon to PLC, at this time it is taking around 30 SEC to update the tag value in PLC. 

    Tags update from PLC to Zenon is taking 5 to 7 sec to update in zenon. I have prioritize the tag update time also. Normal - 300, highest - 100.

    Please suggest how to get fast updation of tags between PLC and Zenon for both read and write. Requirement is tag updation should happen 1 to 2 sec between PLC and zenon.

    What are the factors i have to check in software and hardware? Please suggest and need support on this.

    Regards,

    Dhanapal


  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    845

    Default Re: Zenon to Siemens PLC Tag writing delay

    a delay of 30s could be an indicator of missing write acknowledge.
    Which zenon driver are you using? does this driver supports 'blockwrite' and write acknowledge ('WR_SUC')? You can find this info in the list at the end of the data sheet of driver (in manual or in dialog to create a driver).

    If your RGM recipe is configured to use 'Write synchronously' - try how long it takes if you deactivate it.
    Active: When writing a recipe, all control elements are locked in the Recipegroup Manager screen until the driver confirms that all values have been written successfully or the defined Timeout [ms] has expired.
    I'm suspecting the missing write acknowledge because exactly this timeout in older zenon versions were per default 30s.


    The update times and priorities do not have impact on write to PLC, only on read from PLC (so on update of data in zenon).
    Last edited by ursulak : 22nd August 2018 at 10:23

Similar Threads

  1. Simulate Zenon 6.22 Sp1 Scada on PC with realtime Siemens PLC :-
    By ssmanku1699 in forum zenon Supervisor
    Replies: 0
    Last Post: 8th June 2018, 09:53
  2. Replies: 6
    Last Post: 16th November 2017, 10:57
  3. Writing status bits on Zenon Logic Global Variables
    By maurodx in forum straton / zenon Logic
    Replies: 2
    Last Post: 6th November 2017, 13:26
  4. zenon und Siemens MP370 Touch
    By s.koeppe in forum zenon Operator
    Replies: 3
    Last Post: 26th May 2011, 00:25
  5. Replies: 0
    Last Post: 11th March 2010, 16:04

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •