Thread: Invert read from IED

  1. #1
    Join Date
    19.03.2018
    Posts
    1

    Default Invert read from IED

    Hi guys

    I got a variable that is read from an IED using IEC61850, with a symbolic address to one of the GGIOs. As I need the signal inverted, I'm using the screen Status Definition to invert the visualization. However, I need to send this signal inverted using Modbus...

    Is there any way of reading directly the signal inverted?

    I have another case in which I have a single status signal, but I need to send it as two signals. One of them inverted. So if I could read it inverted, I would be able to use the same symbolic address but one of them inverted...

    Any ideas?

    Thanks in advance

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    971

    Default Re: Invert read from IED

    there are few possibilities, e.g.:
    - you can create second iec850 variable with different name but same symbolic address and link a small VBA macro converting (inverting) values - see variable properties for non-linear value adjustment. Two iec850 variables referring the same symbolic address will work in latest builds of 7.60 and in 8.00 version.
    - you can create variable in MATH driver with a formula converting the value of original iec850 variable, but then the math variable will have data type REAL, probably not optimal for modbus.
    - you can create a zenon Logic project with program converting value of iec850 variable set 'externally visible' and storing it to additional variable of stratonNG driver.
    Solutions with additional calculations in Logic were discussed on Forum.

Similar Threads

  1. Read workspace name from VSTA
    By miguel.martinez in forum VSTA
    Replies: 0
    Last Post: 9th November 2016, 14:19
  2. Connection to IED
    By mehrdad66 in forum zenon Energy Edition
    Replies: 3
    Last Post: 24th October 2014, 09:29
  3. Read I/O from BECKHOFF PLC
    By satyngar in forum Drivers
    Replies: 6
    Last Post: 16th June 2014, 15:44
  4. Invert variable
    By tihomir in forum zenon Service Engine Supervisor
    Replies: 2
    Last Post: 27th May 2013, 18:45
  5. How to invert DPI value and use it in topology coloring.
    By softart2 in forum zenon Energy Edition
    Replies: 1
    Last Post: 7th April 2010, 23:44

Tags for this Thread

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •