    Frage Delta ah500 plc driver

    I am using DELTA PLC and I chose standard modus RTU (open TCP) driver. when I create variables I cannot find data type (WORD/DWORD) under this driver.

    please assist me on this one

  2. #2
    Join Date
    10.12.2007
    Posts
    155

    Default AW: Delta ah500 plc driver

    You must use UINT for WORD (UnsignedINTeger) and UDINT for DWORD (Unsigned DoubleINTeger)