    Hi,

    I have two busbars with two different sources (source Voltage2 at busbar I and Voltage3 at busbar II). A bay is connected to these bus bars with two disconnectors (Q1 and Q2). Furthermore the bay is connected to a transformer (respectively the transformer is a part of the bay). Between the switches and the transformer there is a circuit breaker (Q0) and another disconnector (Q9).
    For the transformer I used a combi-element with ALC function type Transformer. For the Source (Quelle) I choosed the Voltage2 [11] and for the Recovery source (Quelle für Rückspeisung) UNDEFINED [0].
    If the bay is connected to busbar I, the transformer takes over the colour of source Voltage2. But if the bay is connected to busbar II, the transformer doesn’t take over the colour of source Voltage3, because it’s defined that the source is Voltage2.
    I would like to know if it’s possible to change the colour of the transformer without the knowledge of the source. Is it possible to pass the colour/ALC to the other side of the transformer?

    Thank you



    Attached Thumbnails Attached Thumbnails 180513_transformerSource1.png   180513_transformerSource2.png  

  2. #
    Join Date
    28.02.2013
    Posts
    157
    Best Answer

    Default Re: ALC of a transformer with two different sources on different busbars

    Hi ansiem,

    if you want to forward  the color from primary side to secondary side (and not transform it to another source) you could just use a switch.

    Regards,
    Felix

  3. #2
    Join Date
    07.02.2017
    Posts
    10

    Default Re: ALC of a transformer with two different sources on different busbars

    Hi ansiem and welcome to the forum!

    I'm quite curious about the use-case behind this question as redundant busbars usually have the same voltage level; so in your case either Voltage2 or Voltage3, not both. 
    For transformers it's the same - you always transform the voltage from one primary side to 1-2 secondary sides (depending on the transformer type) e.g. 30kV=>13.8kV.
    You can't tell such a transformer to now have 110kV at the primary or secondary side - and this is what you would do in fact.

    Best regards,

    KlemensN


  4. #3
    Join Date
    01.03.2018
    Posts
    6

    Default Re: ALC of a transformer with two different sources on different busbars

    Thank you for your answer.
    The voltage level of both busbars is the same, but I have the case that these busbars are provided by different electrical sources (two different generators). I would like to see which generator feeds the transformer. Of course if the busbars are connected there should be a synchronization. My idea was to create two different ALC sources, which have different colours, but same voltage level.

  5. #4
    Join Date
    28.02.2013
    Posts
    157
    Best Answer

    Default Re: ALC of a transformer with two different sources on different busbars

    Hi ansiem,

    if you want to forward  the color from primary side to secondary side (and not transform it to another source) you could just use a switch.

    Regards,
    Felix

  6. #5
    Join Date
    07.02.2017
    Posts
    10

    Default Re: ALC of a transformer with two different sources on different busbars

    Hi ansiem!

    You already have the information about what is currently feeding your transformer:
    - If feed-forward then it is the ALC source (or the ALC-sources if multiple supply) which colours the line straight before the transformer (Nr. 1 in the figure attached if feed-forward)
    - In reverse feed it is the same but with other direction

    The output side of the transformer (Nr. 2 in the figure attached if feed-forward) however does not care about what source currently feeds the transformer, it always supplies connected ALC-lines with the source defined within the ALC-configuration of the transformer depending of feeding-direction, e.g.:

    - Transformer A is fed in forwards direction by Voltage2 and transforms to Voltage3 => input: Voltage2, output: Voltage3
    - Transformer A is reverse-fed by Voltage3 and transforms to Voltage2 => input: Voltage3, output: Voltage2



    You do not use transformers for passing-through ALC-sources without transforming to different voltage levels; so I can only promote Felix' answer to use a switch instead of a transformer.

    Best regards,
    KlemensN
    Attached Thumbnails Attached Thumbnails 180513_transformerSource2.png  

Similar Threads

  1. ALC Source
    By mytom in forum zenon Energy Edition
    Replies: 2
    Last Post: 24th October 2017, 09:59
  2. Three winding transformer
    By m.sverko in forum zenon Energy Edition
    Replies: 2
    Last Post: 2nd February 2017, 08:55
  3. Replies: 5
    Last Post: 16th July 2014, 12:07
  4. T-Junction of Lines fed by two Sources (ALC)
    By shikra in forum zenon Energy Edition
    Replies: 5
    Last Post: 15th April 2010, 00:35
  5. ALC interlocking
    By gz0000 in forum zenon Energy Edition
    Replies: 1
    Last Post: 7th October 2009, 08:44

Tags for this Thread

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •