Thread: Process Gateway OPC UA namespace problem

  1. #1
    Join Date
    06.04.2018
    Posts
    2

    Default Process Gateway OPC UA namespace problem

    Hi all,

    we are running a SICAM 230 7.00 and currently had Process Gateway installed by our supplier to get OPC UA access to SICAM's tags. There are approx. 3000 tags we added to the OPC UA address space which automatically got the namespace index 80.
    When connecting to the OPC UA server with UaExpert client we are able to browse the server and see all required values. But now there's our data acquisition software, which requires the written namespace URI in its configuration - but it seems that no URI for namespace 80 exists. There are only entries for namespaces 0, 1, 2 in the server's NamespaceArray:
    Click image for larger version

Name:	namespace.JPG
Views:	8
Size:	22.8 KB
ID:	2276
    So how is the URI of namespace 80? Or what other options do we have? Can the tags be transferred to one of the exisiting namespaces? How would that be done without having to change the namespace index manually for 3000 tags in the Process Gateway's variable configuration?

    Thank you for any advice.
    Best regards,
    mirko
    Last edited by mirko : 6th April 2018 at 10:13

  2. #2
    Best Answer

    Default Re: Process Gateway OPC UA namespace problem

    Hello Mirko,

    Thanks for your post and welcome to the forum!

    It is a known issue in 7.00 that there is no entry in the server NamespaceArray for the index 80. Most OPC UA clients can handle this situation.

    What you can try is use notepad to open the file zenprocgateway.ini (use windows explorer to open the directory %cd_system%) that stores your OPC UA server address space configuration.

    Then use search / replace to change the namespace for the variables from 80 to 2. (search for "=80:" and replace with "=2:". This will change the namespace of the variables to 2. Some pre-defined folders however will remain in the server address space with namespace 80.

    Make sure to create a backup of the file prior to editing, in case something goes wrong.

    Best regards,
    Mark

  3. #3
    Join Date
    06.04.2018
    Posts
    2

    Default Re: Process Gateway OPC UA namespace problem

    Hi Mark,

    thank you for this quick and helpful answer. This seems to work and solves our problem!

    Have a nice weekend,
    mirko

Similar Threads

  1. Zenon Process Gateway Communication Problem
    By aniket1993 in forum Drivers
    Replies: 0
    Last Post: 24th February 2018, 04:42
  2. Problem Process Gateway with GE SCADA software GENe
    By mytom in forum zenon Energy Edition
    Replies: 1
    Last Post: 19th January 2018, 09:32
  3. Process Gateway: OPC to another protocol
    By dcs.engineer in forum zenon Energy Edition
    Replies: 6
    Last Post: 10th August 2016, 13:26
  4. Process Gateway
    By mehrdad66 in forum zenon Energy Edition
    Replies: 2
    Last Post: 30th October 2014, 19:28
  5. Process Gateway
    By hoscillada in forum Drivers
    Replies: 12
    Last Post: 8th November 2009, 22:57

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •