Hello sirs,
Sorry for my english I speak just a little.
I have to realize a SCADA for many substations using SIPROTEC 5 7SJ82.
I'm using the program SCADA called ZenOn Energy Edition for the IEC 61850 communication.
I can do everything I need like visualization the state of switchs, verifiy the communication and watch variables and informations (import variables).
But I have an issue with the control process for open and close with the SCADA.
I'm using the variable *CSWI*Pos*Oper.ctlVal*[CO]* for command the SIPRO.
It receives the order (I see in the log the information like "there is a command request") but it doesn't move...
I called SigmaControl (vendors of ZenOn) and they told me to activate the "qualifier command" in ZenOn (value 0, 1, 2 or 3 for inter lock, synchro lock, both lock or no lock) => variable Oper.check i think but it doesn't matter.
I tried with all parameters and nothing happened...
The SIPROTECS are in remote control so I think it's ok.
Can you help me with that issue please.
It's another person who program the IEDs with DIGSI but I can communicate with him if it's necessary. I'm just programming the SCADA ZenOn.
Thank you so much.
Gabriel Simon
gabriel.simon@engie.com
PS: I'm suing ZenOn EE 7.60 SP0 with Windows 10 Pro Server 64 bits mode
PPS: I can send you a backup of the project if you want.