Thread: Driver Mode Switching recommendation?

  1. #1

    Default Driver Mode Switching recommendation?

    Dear Team,

    I'm using Zenon 7.50 Build 49034 and multi-project structure with Three different drivers. I want to stop communication when no communication from controller kindly suggest Driver Mode switching Functions

    1.For starting Driver ----> a) Driver in hardware mode   or  b) Start driver online mode         

    2.For stopping Driver ---->a) Driver in simulation mode or b) Stop driver offline mode


    and kindly suggest recommended settings for "OPC UA Client driver".

    Regards

    Srikanth G





  2. #2

    Default Re: Driver Mode Switching recommendation?

    Hi Srikanth G,

    Stop Driver / Start driver commands can be used to control the driver if you want to stop the communication or start the communication. With simulation mode, the variables will have a SPONT status and may have some other value than 0.

    What is the reason behind this? Can you explain the use case?

    Best regards,
    Mark

  3. #3

    Default Re: Driver Mode Switching recommendation?

    Dear Mark,

    Thanks for your solution regarding 
    Driver Mode selection.

    I have been using "OPC UA Client driver" but found disconnection from DA randomly , but if i restart Zenon Run-time then i have changed setting in driver configuration as image attached.

    then when i start runtime all OPC driver are starting ping (shows in DiagViewer) communication making Run-time hang for 2-3 min. So i wish to stop driver when communication fails for OPC UA, MEI A-Q driver and Zenon Remote Runtime drivers.

    Warm Regards

    Srikanth G  
    Attached Thumbnails Attached Thumbnails OPC.png  

  4. #4

    Default Re: Driver Mode Switching recommendation?

    Hi Srikanth G ,

    With an update interval of 500ms, try setting the keep alive to 20 and the lifetime count to 60, for more tolerance of intermittent delays on the OPC UA server side.

    Best regards,
    Mark

Similar Threads

  1. Language Switching DIALOGKBD
    By EdgyUsername in forum zenon Supervisor
    Replies: 3
    Last Post: 5th February 2019, 09:45
  2. Modbus Driver not switching between adapters
    By Mustafa.SA in forum zenon Energy Edition
    Replies: 5
    Last Post: 16th May 2018, 10:49
  3. Switching variables in Report
    By a.oprean in forum zenon Supervisor
    Replies: 4
    Last Post: 15th January 2013, 02:05
  4. OPC Client driver in synchronous mode
    By micko in forum Drivers
    Replies: 3
    Last Post: 22nd November 2010, 23:27
  5. 6.50: Changing driver mode via VBA
    By herberto in forum VBA
    Replies: 0
    Last Post: 3rd December 2009, 15:27

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •