    Default Zenon OPC UA Client driver

    Hello,
    i tried to connect the ua Client Driver with the OPC UA Server of a Simotion. However, while importing variables from the Server a error message pops up with the Content:

    "Failed to evaluate data types at SIMOTION!
    Failed to read data types: The request could not processed
    because it specified too many operations. (0x80100000)"

    I don´t understand, if the data types or the number of variables (ca 160000) is the Problem.
    And how can i reduce the number of variables, which I want to Import?

    Best Regards!

  2. #2

    Default Re: Zenon OPC UA Client driver

    Hi s.koebler,

    This answer is probably way too late for your request, however the topic comes up every now and then and it helps people find an answer themselves.

    Some OPC UA servers limit the amount of items that can be included in a request so that the request can still be processed efficiently and timely. OPC UA servers can choose to expose the information what amount they support for individual operations in their OPC UA server address space, (OperationLimits) for clients to consider.

    Please make sure you are using the latest version of the OPCUA32 client driver. Here you will find a setting in the driver configuration, for the OPCUA32 driver to consider the server OperationLimits as well as configurable OperationLimits for individual operations, in case the OPC UA server does not expose this information.

    Best regards,
    Mark

  3. #3
    Join Date
    25.08.2019
    Posts
    2

    Default Re: Zenon OPC UA Client driver

    Quote Originally Posted by s.koebler View Post
    Hello,
    i tried to connect the ua Client Driver with the OPC UA Server of a Simotion. However, while importing variables from the Server a error message pops up with the Content:

    "Failed to evaluate data types at SIMOTION!
    Failed to read data types: The request could not processed
    because it specified too many operations. (0x80100000)" 192-168-1-1ip.biz

    I don´t understand, if the data types or the number of variables (ca 160000) is the Problem.
    And how can i reduce the number of variables, which I want to Import?

    Best Regards!
    I was having the same problem. I solved the problem by updating the driver.

    Best regards.

Similar Threads

  1. Zenon OPC UA client out of memory
    By bbo in forum Drivers
    Replies: 1
    Last Post: 7th March 2016, 09:07
  2. OPC Client
    By hohlbauch_pilz in forum zenon Operator
    Replies: 5
    Last Post: 27th September 2013, 17:49
  3. OPC Client configuration
    By luca.bardon in forum Drivers
    Replies: 12
    Last Post: 17th October 2012, 10:08
  4. Structure varible using OPC Client V2-0
    By bsneddon in forum Drivers
    Replies: 1
    Last Post: 21st April 2011, 23:49
  5. OPC Client driver in synchronous mode
    By micko in forum Drivers
    Replies: 3
    Last Post: 22nd November 2010, 23:27

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •