Thread: Status variable for alarm areas

  1. #1

    Default Status variable for alarm areas

    6.22 SP0: when I want to insert a variable for an alarm area as status variable,
    zenon seeks for a boolean variable, but it must be a byte one.
    So the solution is to change the variable to boolean, insert it and
    change back to byte.

    Ist this bug solved in SP1 anyhow?

    Jürgen Berger

  2. #2

    Default Re: Status variable for alarm areas

    Yes this has been a bug which is solved and available with the SP1 of zenon 6.22!

    Your approach to circumvent the situation was pretty perfect.

  3. #3

    Daumen hoch AW: Status variable for alarm areas

    Thanks for quick reply!

    Jürgen Berger