Thread: Alarm Status Line and Alarm List

  1. #1
    Join Date
    22.08.2007
    Posts
    20

    Frage Alarm Status Line and Alarm List

    Hello,
    I have two questions on this topic.
    1) Is there any way how to adjust the background color of status alarm line according to the alarm class (e.g. Faults - red, Warnings - orange, etc.)?
    2) Is it possible to set, that the oldest unacknowledged alarm is always selected in the alarm list (it means that I am always at the top of the list)?

    Thanks for any answers.

  2. #2

    Default Re: Alarm Status Line and Alarm List

    to 1): no, the color of the alarm statusline is always a red background and black text. You can however change the font of the alarm status line.

    Also in 6.22 the position of the alarm status line can be changed in the template editor.

    to 2): in zenon, always the latest alarm is shown in the alarm list, when opening the picture. Of course, you can set a filter to only show unacknowledged alarms.

    For the alarm status line, it can be defined if the oldest unacknowledged alarm is shown, or the latest. Also it can be defined if the statusline should contain all unacknowedged alarms or only the oldest or the newest.

Similar Threads

  1. Alarm Sounds
    By allmendinger in forum zenon Supervisor
    Replies: 5
    Last Post: 27th January 2010, 14:37
  2. Alarm Banner
    By allmendinger in forum zenon Supervisor
    Replies: 1
    Last Post: 17th September 2008, 17:07
  3. Limiting Alarm-status line to one monitor
    By micko in forum zenon Supervisor
    Replies: 1
    Last Post: 15th September 2008, 13:20
  4. Alarm Handling
    By tomaslipa in forum zenon Supervisor
    Replies: 1
    Last Post: 15th September 2008, 13:07
  5. Replies: 3
    Last Post: 7th February 2008, 16:55

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •