In the PLC I have three octets for the IOA address. However in zenOn at the addressing information, only IOA1 is available. How do I address e.g. the Double Command (DCO, Type 46) correctly
in zenOn, all the IOA fields are stored in one field, IOA1. There is a small conversion of the IOAs in the PLC to do, to find the correct addressing information for zenOn.

Example:

in PLC: IOA1 = 196, IOA2 = 135, IOA3 = 0

in hex: C4, 87, 0
in reverse order: 0 87 C4
converted to a decimal number: 34756

IOA1 in zenOn: 34756