Thread: Iec61850 client - too much connection

  1. #1
    Join Date
    10.02.2015
    Posts
    47

    Default Iec61850 client - too much connection

    Hi,
    I have a problem in zenon logic using a iec61850 client.
    I have this driver in the project, with ten connections to RTUs, all equals (only difference is the ip address).
    In total the project has 10000 variables.
    Problem is very strange. After the startup, only few RTUs are connected to the driver, other remain in "connecting mode". If i reboot zenon logic project, other RTUs are connected, different from the RTUs connected before the rebooting.
    I think this problem occurs because there are to much connections and zenon logic doesn't manage all data.
    If i turn off all rtus, then turn on only one in the network, zenon logic reaches immediately it.
    Do you have any solution?
    I can't create two istance of zenon logic. One one project is allowed.
    Other information: i have monitored ConnectionState variables in zenon logic. RTUs connected have ConnectionState = 65538 (integer value)
    RTUs non connected, instead - ConnectionState = 2. So in all cases, all RTUs are connected in tcp/ip but RTUs with ConnectionState equal to 2 doesn't communicate in 61850.
    I need your help, zenon logic is getting me in much troubles.

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    995

    Default Re: Iec61850 client - too much connection

    >ten connections to RTUs, all equals (only difference is the ip address).
    I hope these ten connections are using different ‚Server ID‘ setting, and not only different IP. The ‘Server ID’ number must be unique - different per each connection. The described behavior looks like conflict on Server ID or timing problem.

    >In total the project has 10000 variables.
    How many variables are in Reports? By this quantity of variables you have to acquire most variables via Reporting or set 'polling rate' slow.

    In Logic all not reported variables are polled all the time. So the driver, in period defined in ‘polling rate’, tries to actively read from RTUs these variables, which the RTU is not delivering spontaneously - not via URCB, nor BRCB. You may try to set ‘polling rate’ longer, e.g. 60s. Only if then it works - you may try to set shorter.

    Unlike in zenon, in zenon Logic all variables are always “advised”, so the driver has to deliver updates of whole data, and it polls it all the time...

    In IEC61850 driver make sure that you have configured the use of RCBs delivering data (variables) you are using in your project.
    And remove from your project variables you do not need.

    If there is no suitable RCBs on the RTU and possible to reconfigure RTUs - then configure these RTUs to deliver the data you need - in Data Sets linked by RCBs. This demands changes in CID-file of devices and upload into RTUs.

    > RTUs connected have ConnectionState = 65538
    This is when OK - is bit 1 and 16 - means that TCP connection is established (bit 1) and MMS is associated (bit 16). IEC61850 protocol uses MMS and MMS protocol uses TCP. So when connection starts: first TCP is established, then MMS associated (client checks on device the data model, it can take long), then driver enables RCBs and you have working connection.

    > RTUs non connected, instead - ConnectionState = 2
    This is when it was possible to open TCP socket but the association on MMS is not completed. Maybe driver is too busy polling other connections to continue this one or RTU is not reacting correctly.

    If this problem is not caused by missing use of reporting then a Wireshark sniff could be helpful.

  3. #3
    Join Date
    10.02.2015
    Posts
    47

    Default Re: Iec61850 client - too much connection

    I solved modifing RTU software. It wasn't optimized. In particular: in old rtu software I mapped all signals ( a very amount of stuff), now I mapped only signals I have to use in Zenon Logic.

  4. #4
    Join Date
    08.12.2015
    Posts
    39

    Default Re: Iec61850 client - too much connection

    Hi,
    Ok great, thank you for your feedback !

Similar Threads

  1. Connection to IED
    By mehrdad66 in forum zenon Energy Edition
    Replies: 3
    Last Post: 24th October 2014, 09:29
  2. Connection to zenon
    By churras in forum Engineering Studio Logic & Logic Service (former zenon Logic Workbench & Runtime)
    Replies: 5
    Last Post: 4th August 2014, 12:01
  3. Zenon server & Client Connection
    By sidramsatyal in forum zenon Network
    Replies: 3
    Last Post: 7th July 2014, 13:26
  4. WebServer - Client Connection
    By abcd1234 in forum Smart Server & Smart Client (former Webserver & Webclient)
    Replies: 0
    Last Post: 13th January 2014, 19:35
  5. Winsock connection
    By michael_k in forum Drivers
    Replies: 1
    Last Post: 26th March 2012, 23:48

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •