Thread: IEC 60870-5-103 command & response

  1. #1
    Join Date
    19.10.2013
    Posts
    1

    Unglücklich IEC 60870-5-103 command & response

    Hi,
    How to create a command with a variable is double indication and double command.
    In IEC103, value OFF, ON is 1, 2, not 0, 1 and I can not active write set values.
    I have created a command but could not. I using the SIEMENS 7SJ62 relay.

    Thanks,
    Lang
    Attached Thumbnails Attached Thumbnails 01.png   02.png  
    Last edited by softvn : 30th September 2015 at 03:52

  2. #2

    Default Re: IEC 60870-5-103 command & response

    Hi softvn,

    Thanks for your post and welcome to the forum!

    From your screenshot, I can see that the driver object type is set to MONITORING. Please try and change this to "COMMAND"

    After changing this, you could try first, to remove the command group and write directly to the variable.

    When direct writing is working correctly, you can then configure the command input by linking the command group at the command variable and the response variable and configuring the command groups accordingly.

    Best regards,
    Mark

Similar Threads

  1. IEC 870-103 driver
    By mytom in forum zenon Energy Edition
    Replies: 12
    Last Post: 11th February 2019, 13:56
  2. GI in IEC 60870-5-104
    By knubla in forum zenon Energy Edition
    Replies: 1
    Last Post: 7th February 2018, 14:51
  3. IEC 60870-5-103 private ASDU
    By okhotnikov in forum zenon Energy Edition
    Replies: 4
    Last Post: 1st September 2015, 11:02
  4. IEC 103 Distrubance Record
    By archie in forum zenon Energy Edition
    Replies: 13
    Last Post: 13th September 2012, 10:08

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •