Thread: GI in IEC 60870-5-104

  1. #1
    Join Date
    22.10.2012
    Posts
    25

    Default GI in IEC 60870-5-104

    Hi,
    we have the attached XML document with 104 communication. We start the connection without problems (STARTDT_ACT, STARTDT_CON) but when we request a general interrogation (GI) we start to receive data (simple points, double points, measurements) but we don't receive the termination confirmation for this request. That's a problem because the master will not know when the data transfer has finished. Have you any idea why the Process Gateway does not send this termination confirmation?
    Regards.
    Attached Files Attached Files

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,039

    Default Re: GI in IEC 60870-5-104

    there are 2 very typical reasons why zenon Process Gateway IEC870Slave cannot terminate the General Interrogation:

    - when it does not have values for some of zenon variables configured to be IOs. This scenario is a configuration mismatch; it may happen when e.g. a variable which is in zenon a command (so 'write-only' in iec870, iec850 or DNP3 driver) is mistakenly configured in zenPG as an IO in monitoring, not control, direction. As in zenon, after project start, 'write-only' variables are "empty" until the user gives the first command (sets the value for the first time), the zenPG does not know what it should send to a remote master. Then GI will stay open "forever".

    - when the remote master sends new GI before the previous GI is completed. If the master sends a further GI while the current one has not yet been concluded, the ongoing GI is canceled and the new one is started. Overlapping GIs are logged as a warning. This is an indication of non-Standard-compliant behavior of the master.

Similar Threads

  1. IEC 60870-5-104-Time stamp problem
    By xeren in forum zenon Energy Edition
    Replies: 3
    Last Post: 15th July 2015, 12:33
  2. IEC 60870-5-104 Driver
    By xeren in forum zenon Energy Edition
    Replies: 1
    Last Post: 19th July 2013, 09:38
  3. IEC 60870-5-104 standard
    By xeren in forum Engineering Studio Logic & Logic Service (former zenon Logic Workbench & Runtime)
    Replies: 5
    Last Post: 15th May 2013, 13:28
  4. IEC 60870-104 Slave in Straton
    By altera in forum Engineering Studio Logic & Logic Service (former zenon Logic Workbench & Runtime)
    Replies: 3
    Last Post: 15th October 2012, 12:14
  5. Many questions about IEC 60870-104
    By focus in forum zenon Energy Edition
    Replies: 1
    Last Post: 11th July 2011, 08:45

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •