    I am using zenon to communicate with Beckhoff PLC. I am able to communicate plc driver variables between the two. Can you please advise me how zenon system variables can be communicated to the PLC.

    Many thanks in advance!

  2. #2

    Default Re: zenon logic doesn't communicate with external variables in zenon

    Hi anjali.gk.nair,

    You could create an allocation in the editor and link as the source variable the system driver variable and a beckhoff PLC variable as the target variable.

    When the system driver variable changes, the PLC variable will be written.

    Best regards,
    Mark

  3. #3

    Default Re: zenon logic doesn't communicate with external variables in zenon

    Thank you very much Mark!

Similar Threads

  1. zenon logic doesn't communicate with external variables in zenon
    By mashjj in forum straton / zenon Logic
    Replies: 6
    Last Post: 27th February 2015, 13:10
  2. Zenon logic
    By sidramsatyal in forum straton / zenon Logic
    Replies: 0
    Last Post: 1st July 2014, 09:45
  3. Minimal external variable change interval to be hooked in zenOn
    By stolyarov_as in forum zenon Supervisor
    Replies: 1
    Last Post: 24th September 2013, 18:38
  4. External IEC 60850 variables names not recognised in ZenonLogic
    By djgaunt in forum straton / zenon Logic
    Replies: 3
    Last Post: 12th August 2013, 07:53
  5. Zenon Logic Redundancy
    By davide.galigani in forum straton / zenon Logic
    Replies: 3
    Last Post: 24th April 2013, 07:22

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •