Thread: Tapcon commands with 61850

  1. #1
    Join Date
    09.04.2013
    Posts
    57

    Default Tapcon commands with 61850

    Hi,
    does anybody know how to set command raise/lower for tapcon on Zenon HMI?
    Tapcon expects values 1/2, but I can only set 0/1 because command variable (xxx.ATCC1.LTCBlk.ctlVal) is BOOL and it can not be changed.

    Please help, I have urgent situation on site.
    Regards.

  2. #2
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    1,033

    Default Re: Tapcon commands with 61850

    I do not know tapcon, but i hope its data model and behavior follows rules of the IEC61850 Standard . According the Standard in logical node ATCC there are data objects LTCBlkVLo, LTCBlkVHi and LTCBlkAHi and they are not dedicated to give commands. And there is no just LTCBlk at all. So, the object reference in your post - xxx.ATCC1.LTCBlk.ctlVal - is very strange. Are you sure you created the variables by online, eventually offline import from tapcon/its SCL-file? By manually created variables it is easy to make some mistake, so we strictly recommend to use online import; eventually offline, not manual creation of variables. By online import - do you see any *Oper.ctlVal[CO] items in this ATCC? To give a legal command you need variable *Oper.ctlVal with FC=CO or SP.

    A general explanation: to give a command you have to use data objects of a class supporting Control services. I see in the IEC60850-7-4 Standard the LTCBlk* are in class SPS (no 'Controls'). According Standard there is no ctlVal attribute in SPS and a Control always includes the whole Oper attribute - which is a structure, thus */Oper.ctlVal (and not single ctlVal).

    According the 850-7-4 the logical node ATCC has few legal 'Controls'. I suppose the suitable would be: data object TapChg - 'Change tap position (stop, higher, lower)' or TapPos - 'Set tap position'. These objects are in class BSC having data attribute Oper. Does the tapcon have such items in its data model?
    When yes, then the suitable command variable in zenon would be */ATCC1/TapChg/Oper.ctlVal[CO] or */ATCC1/TapPos/Oper.ctlVal[CO] where ctlVal is a numerical value ('CODED ENUM') - stop | lower | higher | reserved; for sure not BOOL when online/offline imported.

  3. #3
    Join Date
    09.04.2013
    Posts
    57

    Default Re: Tapcon commands with 61850

    Hi Ursula,
    thx for reply.

    It seems that there was too much manual work here.
    After repeated import, it works.

    Thanks again.
    Regards.

  4. #4

    Default Re: Tapcon commands with 61850

    Hi timohir
    Please can u tell me how to establish communication zenon and tapcon 260
    Because i try To communicate with online method i can get the variables but in runtime mode i cant not read the values of this variables
    Best regards
    Dahmane

Similar Threads

  1. IEC 61850 Error
    By yara in forum zenon Energy Edition
    Replies: 2
    Last Post: 3rd June 2014, 09:37
  2. 61850 Server
    By junior in forum Engineering Studio Logic & Logic Service (former zenon Logic Workbench & Runtime)
    Replies: 2
    Last Post: 13th March 2014, 12:48
  3. Regarding to SOE of IEC 61850
    By gyu in forum zenon Energy Edition
    Replies: 1
    Last Post: 11th March 2014, 09:45
  4. Problem with IEC 61850 reports
    By lucarocca in forum zenon Energy Edition
    Replies: 1
    Last Post: 18th December 2013, 13:03
  5. Problem with 61850 driver
    By shahrzad in forum zenon Energy Edition
    Replies: 1
    Last Post: 31st August 2009, 02:34

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •