Thread: Event list

  1. #1
    Join Date
    20.03.2013
    Posts
    25

    Default Event list

    IEC60870/ Zenon 7.00 SP0 build4
    I have an input point e.g. P120_1: single point information and spontaneous, CAOA: 1, IOA: 2
    If I use this configuration, I can see it in Zenon Events list.
    If I change input point e.g. P120_1: single point info with time tag CP56Time2a and spontaneous, CAOA: 1, IOA: 2.
    In this case, I canít see it in Zenon Events list
    But if I use triangle I can that is work fine.
    Attached Thumbnails Attached Thumbnails Triangle.jpg  

  2. #2
    Join Date
    20.03.2013
    Posts
    25

    Default Event list

    IEC60870/ Zenon 7.00 SP0 build4
    I have an input point e.g. P120_1: single point information and spontaneous, CAOA: 1, IOA: 1
    If I use this configuration, I can see it in Zenon Events list.
    If I change input point e.g. P120_1: single point info with time tag CP56Time2a and spontaneous offline buffered, CAOA: 1, IOA: 1.
    In this case, I canít see it in Zenon Events list.
    But if I use the application Triangle, everything work fine
    Attached Thumbnails Attached Thumbnails Triangle.jpg  
    Last edited by xeren : 22nd October 2013 at 15:50 Reason: error

  3. #3
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    801

    Default Re: Event list

    When an information object (IO) without any time tag changes value then the event has no time information and when iec870 master receives it (in zenon) then gives the variable value the timestamp from the moment of reception, from local PC clock. And you can see it.

    When an IO with "time tag CP...." changes value then the event has timestamp given by slave (PLC/device). Then the variable value in zenon has timestamp not from local clock but from time information sent by slave - on additional bytes - in the frame with event value. You don't see them...

    ...So your problem is that you don't see in zenon values with external timestamps. I suppose the values are there, but somewhere in the past or in the future; out of the range your filter settings.

    Solution:
    Synchronize clock of the slave with the clock of the PC with zenon. Make sure both are using the same 'daylight saving' option. The time tag CP56Time2a does not contain daylight saving information, so the mismatch shifts data by one hour; during summer time. (or wait one week then for few months will be OK )

  4. #4
    Join Date
    20.03.2013
    Posts
    25

    Default Re: Event list

    Thanks for answer,
    I was thinking that values were somewhere in the past or in the future; out of the range our filter settings, but the filter is 2 days. So I think that the problem somewhere else, i can even remove this filter.
    Attached Thumbnails Attached Thumbnails filter_time.jpg  

  5. #5
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    801

    Default Re: Event list

    if this slave is sending the data and the addresing in zenon is correct (is it?) then the events are for sure in zenon, just with wrong date and/or time. Maybe you are showing in filter only entries from ring-buffer, and not historical, or the filter is set to show too less quantity of entries etc.
    Last edited by ursulak : 24th October 2013 at 07:20

Similar Threads

  1. Replies: 10
    Last Post: 20th October 2013, 23:53
  2. Deleting Chronologic Event List
    By navaneet in forum zenon Supervisor
    Replies: 1
    Last Post: 7th October 2013, 22:54
  3. Event list classes and internal system messages
    By softart2 in forum zenon Supervisor
    Replies: 3
    Last Post: 19th May 2011, 05:59
  4. Log changes into cronologic event list (CEL)
    By hicom in forum zenon Supervisor
    Replies: 6
    Last Post: 8th April 2009, 07:22

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •