Showing results 1 to 8 of 8

Thread: Siemens PLCSim

  1. #1
    gh_ounie Gast

    Frage Siemens PLCSim

    Hi MarkClemens
    I have a Zenon software for touch screen and PLCSim from Siemens...
    i just wanna know if is posible to work togheter...thank you

  2. #2

    Default Re: Siemens PLCSim

    unfortunately, Siemens PLCSim does not communicate with zenOn. Although zenOn communicates to almost all Siemens PLC hardware, PLCSim seems to be working only with Siemens software.

  3. #3

    Idee Re: Siemens PLCSim

    Hello,

    I have heard that the communication between PLCSim and zenon is possible when you use "NetToPLCSim".
    You can download this program here:

    http://nettoplcsim.sourceforge.net/

  4. #4

    Default AW: Siemens PLCSim

    Hallo,

    ich habe NetToPLCSim gerade im Einsatz:

    das Lesen und Schreiben von Datenbausteinen funktioniert einwandfrei, allerdings werden Ein-/Ausgänge mit roten Klötzchen (Variable nicht lesbar) in zenOn dargestellt.

    Ferner funktioniert PDiag nicht.

    Der Entwickler von NetToPLCSim ist leider nicht erreichbar, die Emailadresse th.wiens@gmx.de ist leider tot.

    Wer weiß Abhilfe?
    zenOn Version: 6.51 SP0 Build 0

  5. #5
    Join Date
    27.01.2011
    Posts
    1

    Default Re: AW: Siemens PLCSim

    Das hier habe ich von ihm im SPS-Forum gefunden:
    Einzige Einschränkung bei der PLCSim Anbindung ist aber dass nur Merker und Datenbausteine gelesen werden können. Das liegt aber an der beschränkten OCX-Schnittstelle zu PLCSim.
    scheint also nicht zu gehen mit einfachen E/As

  6. #6
    Join Date
    03.09.2014
    Posts
    1

    Default AW: Siemens PLCSim

    Tested, working!
    Zenon 7.00 SP0 build 9 with NetToPLCSim 0.9.4

  7. #7
    Join Date
    06.08.2018
    Posts
    3

    Frage Re: Siemens PLCSim

    Hi folks,
    any lucky man who succeeded connecting TIA V15 PLCSIM 1500 to zenon 7.60 S7TIA driver?
    For me the connection is always refused, using NetToPLC 1.2.4.0

    Any suggestions will be very appreciated.

    thanks.

    Response error chunk form WireShark:

    Click image for larger version

Name:	wireshark plcsim.png
Views:	9
Size:	16.0 KB
ID:	2635
    Last edited by zendesk : 12th July 2019 at 14:10 Reason: wireshark

  8. #8
    Join Date
    06.08.2018
    Posts
    3

    Frage Re: Siemens PLCSim

    The error reported by DiagViewer on S7TIA instance is:

    Code:
    Error FFFA0195 (Wrong read type) in AGL_PLCConnect
    After about 10 seconds running S7TIA driver crashes with this report:

    zenOn Version: 8.10 SP0 Build57250
    Processor: x86
    //-----------------------------------------------------
    Exception code: C0000005 ACCESS_VIOLATION
    Fault address:  664A2F02 01:000E1F02 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll

    Registers:
    EAX:00000000
    EBX:04EBFCB4
    ECX:00000000
    EDX:00000000
    ESI:035FD330
    EDI:00000000
    CS:EIP:0023:664A2F02
    SS:ESP:002B:04EBFC94  EBP:04EBFC98
    DS:002B  ES:002B  FS:0053  GS:002B
    Flags:00010293

    Call stack:
    Address   Frame     Logical addr  Module
    664A2F02  04EBFC98  0001:000E1F02 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    664A33A0  04EBFCE4  0001:000E23A0 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    664A6C5F  04EBFD34  0001:000E5C5F C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    664A6B37  04EBFD68  0001:000E5B37 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    66471DB1  04EBFEB4  0001:000B0DB1 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    6641D094  04EBFF30  0001:0005C094 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    66448089  04EBFF3C  0001:00087089 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    66650D77  04EBFF74  0001:0028FD77 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    66650E01  04EBFF80  0001:0028FE01 C:\Program Files (x86)\COPA-DATA\zenon 8.10\AGLink40.dll
    76608494  04EBFF94  0001:00008494 C:\WINDOWS\System32\KERNEL32.DLL
    774241C8  04EBFFDC  0001:000631C8 C:\WINDOWS\SYSTEM32\ntdll.dll
    77424198  04EBFFEC  0001:00063198 C:\WINDOWS\SYSTEM32\ntdll.dll

    All works fine with S7TCP driver using PLCSIM Advanced 2.0 pointing a not optimized DB.

    The issue is related to S7TIA only with optimized block access.
    ---
    - both zenon 7.60 and zenon 8.10.
    - TIA Portal 15.0
    - PLCSIM Advanced 2.0