Thread: External IEC 60850 variables names not recognised in ZenonLogic

  1. #1
    Join Date
    29.07.2007
    Posts
    10

    Frage External IEC 60850 variables names not recognised in ZenonLogic

    Hi

    I've made externally visible several IEC 60850 variables so that I can do some data type conversions in ZenonLogic. These will then be allocated to IEC 60870 variables.

    The problem is although the variables are visible in ZenonLogic and values visible in runtime, I'm unable to use them within any program blocks FDB, IL, etc. I'm assuming that the problem is that the variable naming convention for 61850 variables do not comply with the IEC 61131-3 standard. Is it possible to use external 61850 variables in ZenonLogic or am I just missing something obvious here?

    I'm using version 7.00 SP0 build 2 of Zenon.

    Dave
    Last edited by djgaunt : 3rd September 2013 at 11:02

  2. #2

    Default Re: External IEC 60850 variables names not recognised in ZenonLogic

    Hi Dave,

    Depending on the zenon version, you have two or three options available in the driver configuration, where the name for communication to the IEC61850 server is stored.

    When you use the variable identifcation for the communication, you can rename the variable name to a valid name according to the naming conventions in IEC61131-3, and use it in the zenon logic.

    Click image for larger version

Name:	ScreenShot388.png
Views:	41
Size:	12.7 KB
ID:	1169

    Best regards,
    Mark

  3. #3
    Join Date
    30.05.2007
    Posts
    105

    Default Re: External IEC 60850 variables names not recognised in ZenonLogic

    Hi,

    there is another Option.
    You can use the variables as they are in your zenon Logic program, the only thing you need to do, is to put the variables names in { }
    Be Aware of, that you cannot drag&drop these variables into the code. But copy paste the name in the variable box in FBD or copy paste in ST or other language is no problem. Only put it in brackets { }

    see attached screenshot for reference


    Markus
    Attached Thumbnails Attached Thumbnails IEDVars.png   IEDVarFBD.png  
    Last edited by markusw : 12th August 2013 at 07:10

  4. #4
    Join Date
    29.07.2007
    Posts
    10

    Lächeln Re: External IEC 60850 variables names not recognised in ZenonLogic

    Thanks for your quick response guys, much appreciated.

    I knew there must have been a simple solution to this problem.

    I prefer the second solution using the {..} brackets. If I use the first method switching to the identification field for the 61850 address then I would not have a variable description field.

    Of course, I suppose I could always use the resource field for description, but that would require a lot changes to my project.

    Regards

    Dave

Similar Threads

  1. zenon logic doesn't communicate with external variables in zenon
    By mashjj in forum straton / zenon Logic
    Replies: 6
    Last Post: 27th February 2015, 13:10
  2. Replies: 4
    Last Post: 28th August 2012, 00:34
  3. Problem with IEC 104.
    By brada in forum zenon Energy Edition
    Replies: 3
    Last Post: 6th May 2012, 23:58
  4. CLX Variable Names
    By lunzer in forum zenon Supervisor
    Replies: 2
    Last Post: 9th December 2008, 16:29
  5. PLC Variables and Internal Variables
    By madphilly in forum Drivers
    Replies: 1
    Last Post: 4th June 2008, 06:59

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •