Thread: Alarm status line in multimonitor project

  1. #1

    Default Alarm status line in multimonitor project

    Hello colleagues.

    Is it possible (if yes - starting from which version of zenon) to set alarm status line such way that on both monitor it shows same information?
    This question is extended to main menu also.
    See picture in attachement.
    Attached Files Attached Files
    Regards,
    Andrey

  2. #2

    Default Re: Alarm status line in multimonitor project

    Hello,

    as Standard functionallity this is even in the current version (7.10) not available.

    Possible workaround I can imagine:
    • To create an alarm mdi window for each monitor.
    • Configure the mdi window in a way that it appears like an alarm status line
    • Set the alarm appearance accordingly
    • Set the monitor assignment in the screen switch function for each mdi window accordingly