Thread: Zenon Modbus TCP connection to phoenix ILC
    jgv Gast
    Default Zenon Modbus TCP connection to phoenix ILC
    I am trying to connect a phoenix ilc 191 with a suetron windows CE panel running Zenon.
    The controller can act as a slave and i can write or read coils and registers.
    I use the Zenon modbus rtu/tcp driver to be the master.
    The problem is that in the manual of the controller they say :
    For the memory area of the process data item, please
    refer to the documentation of the device that is used as
    a Modbus device.
    So how do i make the connection on both sides the same so i can transfer data from controller --> Zenon RT and inverse.
    Thank you,
    25.06.2012
    155
    Default Re: Zenon Modbus TCP connection to phoenix ILC
    Hi jgv,
    Welcome to COPA-DATA forum! Wish you the best here!
    To connect zenon runtime to a Modbus controller from zenon you need first a driver. The available Modbus drivers can be seen in zenon editor workspace at Variables > Driver > New driver.... The driver must be chosen according, among others, the targeted controller model.
    For more information about drivers you can consult zenon online documentation by pressing F1 and selecting the topic Drivers. Here you will find a list of all zenon drivers, as well as, their respective requirements, configuration procedures, variables creation, etc. I strongly recommend you to read it first.
    After driver configuration is concluded, you need to create and address the variables accordingly the targeted device programming and create screen elements (i.e. Numerical value) in such way you can read/write values from/to PLC in a zenon screen.
    DC
    02.06.2010
    Freiburg
    187
    Default AW: Zenon Modbus TCP connection to phoenix ILC
    you need to know the address space of the variables on the controller. For registers this should be something like %MW, for coils %M. If the address on the controller is for example %MW100, then in zenon the offset should be 100. (In some cases the offset is 99.) - Some manufacturers work with bytes instead of words. In this case %MW100 in the plc refers to offset 50 in zenon.
    Michael
  1. STRATON controling Modbus TCP slave bus controller with IO's
    By barszcz in forum straton / zenon Logic
  2. Phoenix Treiber Frage
    By jusufs in forum Drivers
    Last Post: 5th March 2012, 11:20
  3. Real Variable Modbus TCP
    By pkreisel in forum Drivers
    Last Post: 15th February 2011, 23:39
  4. TCP ports in use by zenOn
    Last Post: 23rd August 2009, 23:18
  5. connection failed between zenOn and STRATON
    By bernhards in forum straton / zenon Logic
    Last Post: 21st August 2007, 07:52