    Frage Beckhoff TwinCat NG driver -> Red square

    I am having the set of machinery running at the downfloor. I would like to create a summary diagnostic screen which will give a brief owerview of the statuses of all machines.
    Each machine runs at Beckhoff1020 CX and having dedicated IP adress.

    Below is the content of Beckhoff TwinCat NG driver.ini
    [LAUFZEITSYSTEME]
    LZS1=801\127.0.0.1.1.1
    LZS2=801\10.67.95.50.1.1
    LZS3=801\10.67.95.57.1.1
    LZS4=801\10.67.95.64.1.1
    LZS5=801\10.67.95.71.1.1
    LZS6=801\10.67.95.78.1.1
    LZS7=801\10.67.95.85.1.1
    LZS8=801\10.67.95.92.1.1
    LZS9=801\10.67.95.99.1.1
    LZS10=801\10.67.95.106.1.1
    LZS11=801\10.67.95.113.1.1
    LZS12=801\10.67.95.120.1.1
    LZS13=801\10.67.95.127.1.1
    [IMPORT]
    OTHER_TARGET_STATION=1
    TPY_PATH=C:\a1.tpy
    TARGET_STATION_NAME=1: NetID[10.67.95.50.1.1], Port[801]
    All stations are having the same variable.
    The issue I am getting is the red squares for almost all stations except 2 stations.

    What I am doing wrong?
    Kind regards,
    Sergiy

  2. #2

    Default Re: Beckhoff TwinCat NG driver -> Red square

    Hi Sergiy,

    There can be a number of things.

    - On the PC with the zenon runtime, install TwinCAT CP
    - On the PC with the zenon runtime, using the TwinCAT system manager, confgure "routes" to all the PLCs. This will create a target AMS Net ID with IP address in the AMS router on the PC with the runtime, but also will it create an allowed client on the PLC side. On the zenon Runtime side, the PLC must be known in the AMS router, and on the PLC side, the zenon Runtime PC must be known in the AMS router.
    - you may need to restart the PC after configuring the "routes"


    Best regards,
    mark

  3. #3
    Join Date
    01.11.2012
    Posts
    60

    Default Re: Beckhoff TwinCat NG driver -> Red square

    Quote Originally Posted by markclemens View Post
    - On the PC with the zenon runtime, using the TwinCAT system manager, confgure "routes" to all the PLCs.
    Yesss! It was the case!
    I were doing this for the TwinCat, but had no Idea that the same is applicable for Zenon driver. Thank you for drawing my attention to that.
    Kind regards,
    Sergiy

Similar Threads

  1. Bug report for <Beckhoff TwinCat NG driver>
    By lephis in forum Drivers
    Replies: 4
    Last Post: 6th March 2012, 10:11
  2. Beckhoff OPC Server
    By anemet in forum Drivers
    Replies: 1
    Last Post: 29th September 2011, 00:18
  3. ZenOn RT starting before TwinCAT on CE
    By davidgrice in forum zenon Service Engine Operator
    Replies: 1
    Last Post: 29th September 2009, 23:29
  4. Beckhoff Buscontroller BC / BK
    By markclemens in forum Drivers
    Replies: 0
    Last Post: 24th February 2009, 09:22
  5. Replies: 5
    Last Post: 16th July 2008, 09:16

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •