Thread: Read Date & Time from Time Attribute on IEC61850

  1. #1
    Join Date
    13.10.2012
    Posts
    21

    Default Read Date & Time from Time Attribute on IEC61850

    Hello,

    I would like to read date and time from variable and display it in numeric field.I am using IEC61850 driver.
    I have tried to do this by mapping the time attribute of that specific variable. When I import the variable in zenOn the data type it is showing is LREAL. The value it is showing in the run-time is difficult to interpret.
    I have also tried to do this by using Allocation. In the allocation source value of this variable was transferred to internal variable having data-type DATE & TIME. But still I could not see the exact value in the Run-time.
    I have tried to read the time attribute of the same variable on different IEC61850 client software where it is displaying the correct date and time.
    What steps I need to following to achieve this in zenOn?
    Thanks.

  2. #2
    Join Date
    25.06.2012
    Posts
    116

    Default Re: Read Date & Time from Time Attribute on IEC61850

    Hello salmanhassan2,

    I would like to read date and time from variable and display it in numeric field.I am using IEC61850 driver.
    You can read this Data-attribute easily by simply using a Clock element assigned to .t DA.

    Are you aware of this?

    Attached a sample project to zenon 7.00.

    Please let us know if this helped you.

    Best regards,
    DC
    Attached Files Attached Files

  3. #3
    Join Date
    13.10.2012
    Posts
    21

    Default Re: Read Date & Time from Time Attribute on IEC61850

    Hello David,
    I did not know this. But thanks, It was quite easy. I have checked the date and time stamp by modifying the value of variable in zenOn logic. I will check it will real time IEC61850 Server also. I believe there won't be any problem. Thanks for the prompt response.

  4. #4
    Join Date
    25.06.2012
    Posts
    116

    Default Re: Read Date & Time from Time Attribute on IEC61850

    You're welcome!

    Best regards,
    DC

  5. #5
    Join Date
    01.07.2008
    Location
    Salzburg, AT
    Posts
    768

    Default Re: Read Date & Time from Time Attribute on IEC61850

    During import zenon creates all LREAL variables with default value range -1000..1000 and no decimal places. So for variables with t-attributes i would recomend you to change the value range to 0..2147483647 and also maybe to set Decimals to 3 - for milliseconds. But note that the clock element does not show milliseconds, to display in a screen also milliseconds you will have to use additional numerical element placed (and partialy hidden) under clock element.

    The easiest way to give for all t-variables correct value range is:
    1. create new simple datatype e.g. "iec850_UTCTime" basing on LREAL
    2. change its properties in Value calculation group for value range and value adjustment range to 0..2147483647, and eventually decimals from 0 to 3.
    3. multi-select all t-variables and change the variable property Data type from LREAL to iec850_UTCTime.

Similar Threads

  1. date and time display using variable
    By paruvathakumar in forum zenon Supervisor
    Replies: 1
    Last Post: 22nd January 2013, 14:58
  2. trying to read system time in plc from sicam
    By imran in forum zenon Supervisor
    Replies: 1
    Last Post: 14th May 2012, 02:28
  3. Changing date & time of a panel during runtime
    By batabaha in forum zenon Operator
    Replies: 1
    Last Post: 15th April 2012, 23:35
  4. Trends Time
    By ziadrached in forum zenon Supervisor
    Replies: 2
    Last Post: 3rd November 2008, 10:26
  5. compare time variable with system time
    By flajoso in forum VBA
    Replies: 7
    Last Post: 25th August 2008, 06:47

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •