Thread: Process gateway(Modbus)

  1. #1

    Default Process gateway(Modbus)

    Hi,

    in process gateway of zenon(7.0), i have noticed that there is only option for setting holding register offset. But i want to configure for read input register in process gateway(function 02h). How do i make this possible?

  2. #2
    Join Date
    30.05.2007
    Location
    Salzburg
    Posts
    879

    Default Re: Process gateway(Modbus)

    please check the help documentation on this:
    Manual -> Process Gateway -> Requirements

    Attention

    If the Modbus Slave driver is used, the Process Gateway only supports:

    Function Code 3: Read Multiple Registers
    Function Code 16: Write Multiple Registers


    regards,
    herbert