The RTU's behavior you've described does not conform to the IEC60870 Standard. Thus, to manage it in the RTU is the only solution.
According the Standard each Information Object in monitor direction must have its own IOA. With other words: any data-point with type identification from range <1..40> must have an unique IOA. And must use ASDU (message) format defined in the Standard.
Also each command - in control direction - must have an unique IOA, but they can have the same IOA as data-points in monitor direction, e.g. a single command can have the same IOA as the responding single-point information, what IMHO is very comfortable.