  1. #1
    Join Date
    10.01.2008
    Location
    Vimmerby / Sweden
    Posts
    11

    Default Driver for Siemens S7-1200

    Hello.

    We have a siemens S7-1200 plc we want to communicate with.
    We already have the S7 TCP-IP driver fore some S7 300, is this the same driver for S7-1200?.
    How should we set the TSAP setting?.
    Is it anny other setting we have to change?

    Zenon 6.51

    Regards
    Peter G
    Last edited by peterg : 16th June 2011 at 13:24

  2. #2

    Default Re: Driver for Siemens S7-1200

    Yes, the S7TCP32 driver can be used to communicate to a S7-1200 PLC.

    For the remote TSAP you need to use "02.01" (01 is the CPU location in the rack)

    In Step7 for the data blocks (DB), you need to deactivate the option "only symbolic addressing" in order for the communication to work.

  3. #3
    Join Date
    13.06.2013
    Posts
    1

    Default Re: Driver for Siemens S7-400

    Hi,

    We have a siemens S7 400 CP 443-1, the problem is i cannot connect zenon 5.50 application. the error is communication disturb when running zenon runtime. is there any settings that i miss or need to be change?

    Which settings should i look for zenon or in simatic net manager?

    thanks and hope you can help me.

    please send me some examples of configuration connecting an application to remote partner.

  4. #4
    Join Date
    30.05.2007
    Posts
    105

    Default Re: Driver for Siemens S7-1200

    Hi ric,

    When communicating with a S7-400 system you have different slot numbers for your CPU location.
    depending if you using a (1)single slot power supply or (2)double slot you need to set the remote TSAP to (1) 02.02 or (2) 02.03

    And, please also consult the driver manual.

    Markus

  5. #5
    Join Date
    06.06.2018
    Posts
    9

    Default Re: Driver for Siemens S7-400

    Dear Ric ,

    I want to communicate with Zenon 6.22 SP1 runtime on a PC with S7 300 plc on profinet / Ethernet port .

    Do I need any card like CP 443-1 in order to establish the communication ? or it can be done without any additional card .

    Waiting for the prompt reply !

    Thanks
    Manku





    Quote Originally Posted by ric_5518 View Post
    Hi,



    We have a siemens S7 400 CP 443-1, the problem is i cannot connect zenon 5.50 application. the error is communication disturb when running zenon runtime. is there any settings that i miss or need to be change?



    Which settings should i look for zenon or in simatic net manager?



    thanks and hope you can help me.



    please send me some examples of configuration connecting an application to remote partner.


  6. #6
    Join Date
    17.04.2019
    Posts
    1

    Default Re: Driver for Siemens S7-1200

    Is the method shared by the members are still useful?

Similar Threads

  1. Siemens PLCSim
    By gh_ounie in forum Drivers
    Replies: 6
    Last Post: 12th July 2019, 13:44
  2. zenon und Siemens MP370 Touch
    By s.koeppe in forum zenon Operator
    Replies: 3
    Last Post: 26th May 2011, 00:25
  3. Reading "M" bits in Siemens
    By scotttee in forum Drivers
    Replies: 1
    Last Post: 24th September 2009, 08:45

Posting Rules

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •