Thread: VBA error after upgrading rpoject to 6.51
    28.08.2009
    26
    Unglücklich VBA error after upgrading rpoject to 6.51
    After upgrading project from 6,50 to 6,51. I have VBA error code '91'.Object variable or With variable block not set.
    The code is
    Private Sub zAlarm_AlarmComes(ByVal obItem As IAlarmItem)
    If DebugLogEnable Then Debug.Print "zAlarm_AlarmComes" & Now
    Dim funkcija As RtFunction
    Set funkcija = thisProject.RtFunctions.Item("Open_Activ_Alarm_Window")
    Dim Alarm_Window As DynPicture
    Set Alarm_Window = thisProject.DynPictures.Item("Activ_Alarm_Window")
    If Not Alarm_Window.Online Then <---Error comes here
    funkcija.Start
    Else
    Alarm_Window.Activate
    End If
    It is very Strange.
    This code works fine in 6,50. !!!
    I don't know how to fix it. And why Alarm_window variable is nothing.
    What diferences between 6.50 and 6.51.
    How to solve this ....
    Please help me..
    879
    Default Re: VBA error after upgrading rpoject to 6.51
    Which build version of zenon 6.51 SP0 do you use?
    There was a problem in certain build versions of zenon 6.51 SP0 when creating a object from a picture by its name.
    This has been fixed with Build5 of 6.51 SP0.
    The scheduled release of this build is 01.06.2011
    28.08.2009
    26
    I use 6.51 SP0 build 4
    879
    check if you have globaly declared "zAlarm" and also set the object....
    Dim WithEvents zAlarm As Alarm
    'procedure is executed on startup of the zenOn runtime
    Private Sub Project_Active()
        'init the alarm object for events
        Set zAlarm = thisProject.Alarm
    -> check out the example in the help documentation at Object Model -> Alarm