Thread: ALC in clients

  1. #1
    Join Date
    04.09.2009
    Posts
    84

    Default ALC in clients

    Dear,

    When a line picks up its color from ALC in the server machine, this change isn't reflected back on the client workstation running the runtime of the same project. Moreover, the change in variable state is also not reflected back in the clients. What could be the reason? I am using Zenon 6.50

  2. #2
    Join Date
    30.05.2007
    Location
    Salzburg
    Posts
    879

    Default Re: ALC in clients

    Are the blue dots displayed at the dynamic elements (i.e. Numerical value) at the client?
    -> if so, the client does not have a connection to the server

    Regards,
    Herbert

  3. #3
    Join Date
    04.09.2009
    Posts
    84

    Default Re: ALC in clients

    Quote Originally Posted by herberto View Post
    Are the blue dots displayed at the dynamic elements (i.e. Numerical value) at the client?
    -> if so, the client does not have a connection to the server

    Regards,
    Herbert
    No, the blue dots are not shown and the client has a very good connection with the server, because if I change a variable set to 'simulation' at server, the change is reflected at the client end also. If I change the state of Combi element (acting as source), the line takes its color from ALC, at the server end, but not at the client end.

  4. #4
    Join Date
    30.05.2007
    Location
    Salzburg
    Posts
    879

    Default Re: ALC in clients

    Which driver do you use?
    If the variables bases on the INTERN driver with the variable setting "Calculation" -> "Local" the variables are treated on each computer seperately.
    -> set this variable property to "Network"

    FYI: for command processing tests with action variable and response variable the Simulation-Driver is the better choice because the addressing of the variables can not be influenced when using the INTERN driver. Check out also the description within the help documenation at Command input -> Power On -> Screen for command input -> Create data points

    Regards,
    Herbert

  5. #5

    Default Re: ALC in clients

    you may also want to check your license on the client, if it includes the optional module ALC. Is automatic line coloring generally working on the client?