Originally Posted by
ursulak
Maybe you are displaying AML screen with some filter, e.g. time, and the not acknowledged alarms are outside the filter range, e.g. too far in the past or ... in the future.
What driver/communication protocol are you using, IEC 61850, IEC 60870, DNP3? The typical devices (IED) in energy are delivering values with time stamps from the device clock. If the device is not correctly time synchronized, then in zenon such variable value could have some future time stamp.
Try to display without time filter.