  1. Re: OnlineVariable -> Ausführung auf jedem Client?

    dann ist wohl die Variable von INTERN Treiber mit Eigenschaft 'Berechnung' = "lokal".
  2. Thread: Screen damage

    by ursulak
    Replies
    2
    Views
    181

    Re: Screen damage

    If you don't have Runtime historical data - recorded AML, CEL, Historians, etc. - you want to keep, then to cleanup the project from corrupt items you can try to make a project backup...
  3. Replies
    2
    Views
    197

    Re: Verschwundener Thread

    sorry. i do not know why georgk had deleted it, probably by mistake while deleting some spam. I've restored it.
  4. Replies
    3
    Views
    16,428

    Re: Start/Stop Arvhive on PLC Trigger

    In reaction matrix - this linked with your recipe load status variable - activate by value 1 the check-box 'treat each change of value as new limit violation'. Or add in rema the evaluation of...
  5. Re: How to communicate easily between both zenon project A and B.

    yes --&gt; the zenon Network. see in Help &gt; Network &gt; Roles of computers &gt; Multi-hierarchical models<br><br>In project A activate project setting 'Network active' and enter in 'Server 1' the name of...
  6. Replies
    1
    Views
    143

    Re: start and stop archive

    in this dialog the settings to link functions are <u>not</u> for functions which are starting or stoping the archiving.&nbsp;They are for additional other functions you want eventually execute while...
  7. Replies
    4
    Views
    172

    [SOLVED] Re: IEC 870-103 driver & command processing

    VBA macros linked by Variable - 'Value calculation' - 'Value adjustment non-linear' are not changing the value in the hardware.
    These macros are only to do a "virtual" mapping between value in the...
  8. Replies
    4
    Views
    172

    [SOLVED] Re: IEC 870-103 driver & command processing

    As I understand your relay expects in commands the value 1 for OFF and the value 2 for ON.
    In Command Processing module the action 'switching command' works with values 0 for OFF and 1 for ON.
    ...
  9. Replies
    4
    Views
    439

    Re: REMA and IEC870 timestamp question.

    The variable setting 'time deviation' is in seconds and&nbsp;it is&nbsp;an absolut value. Thus,&nbsp;e.g. setting value 1.300 means that if external time differs - in past or future -&nbsp;from...
  10. Re: Logic Error - PLC utilization peaked at 156%

    This log is a hint that the program you have written in Logic needs to execute your code sometimes&nbsp;at least 15ms, while is configured to be executed each 10ms. Another reason for longer...
  11. Replies
    4
    Views
    439

    Re: REMA and IEC870 timestamp question.

    The second question I propose you to post in 'Supervisor', is not an EE topic.&nbsp;But better -&nbsp;send the project backup with the description of the problem to your local COPA-DATA support.&nbsp;
  12. Thread: Delete screen

    by ursulak
    Replies
    1
    Views
    273

    Re: Delete screen

    There is no way to convert&nbsp;compiled Runtime project&nbsp;to&nbsp;its&nbsp;original design in Editor.<br>I recommend to&nbsp;make project backups in&nbsp;Editor more frequently. <br><br>If you...
  13. Re: Reaction Matrix with status bit 53, Zenon EE v8.0

    In rema the status bit T_UNSYNC will be possible to evaluate in (future)&nbsp;zenon 8.20.<br>So now you can evaluate this status bit:<br>- in zenon Combined-Element formula<br>- in zenon Interlocking...
  14. Replies
    4
    Views
    439

    Re: REMA and IEC870 timestamp question.

    If a device is communicating via protocol designed for real time data and events, but the&nbsp;device is not time synchronized, then - data is corrupted; no way around. Synchronize or fix the...
  15. Re: IEC 61850 driver problem reading XCBR/Pos/stVal

    I do NOT recommend to deactivate the&nbsp;double point&nbsp;mapping.<br>This is important feature for&nbsp;human safety&nbsp;during equipment operations. And because it is so important -&nbsp;zenon...
  16. Re: IEC 61850 driver problem reading XCBR/Pos/stVal

    The iec850 driver supports for stVal attributes of the bType Dbpos (IEC 61850-6)&nbsp;the feature&nbsp;'<span class="donottranslate">Double Point Value Mapping' ('DPS/DPC mapping').&nbsp;Correctly...
  17. Replies
    4
    Views
    193

    Re: Systemmessages in eventlist

    maybe&nbsp;you have "SICAM230 avslutades" (<em>or similar, i'm not speaking Swedish</em>)&nbsp;defined in the language table?<br><br>zenon by Runtime start and exit writes info CEL (EN)&nbsp;"system...
  18. Replies
    4
    Views
    193

    Re: Systemmessages in eventlist

    Is this a 'system message' or&nbsp;defined as&nbsp;limit&nbsp;by some SYSDRV variable?
  19. Thread: Report viewer

    by ursulak
    Replies
    4
    Views
    438

    Re: Report viewer

    sorry, but Report Viewer is not a functionality/topic specific for Energy Edition. It looks that people reading&nbsp;EE&nbsp;forum have no clue and people eventually knowing Report Viewer are not...
  20. Re: IEC61850 FileTransfer(COMTRADE) With Dynamic Text

    thank you for sharing your solution <img title="Lächeln" class="inlineimg" alt="" src="images/smilies/smile.png" border="0" smilieid="1">
  21. Re: IEC61850 FileTransfer(COMTRADE) With Dynamic Text

    The order in the list is like delivered by the IED. This is like by&nbsp;another string variables received from a device. And&nbsp;there is no "post sorting".&nbsp;You see the real value in...
  22. Replies
    1
    Views
    350

    Re: Function and script

    A&nbsp;script executes (series of) functions. <br>To run a script you have to create a function 'script: execute' and call it in the runtime (e.g. link with button or a variable limit).<br><br>in...
  23. Replies
    3
    Views
    486

    Re: Automatic line coloring issue

    If your project does not behave in the Runtime like expected and you are not founding any topological/configuration mistakes in the Editor - send the project backup and description of the expected vs...
  24. Replies
    1
    Views
    567

    Re: Multiple Channel in same driver

    you can create in sum&nbsp;about 250 process drivers;&nbsp;can be&nbsp;different drivers or instances of the same driver.&nbsp;
  25. Replies
    3
    Views
    486

    Re: Automatic line coloring issue

    I would propose you to make the energy training. It is available also online.